i had 4 Par38 75W bulbs on track. replaced them with 4 led 13W bulbs. all work but last one . i tested bulb on another fixture works fine.? when i put old "incandescent" bulb in last one all works fine the track is on dimmer and all bulbs dim except when led is in last fixture is there limit of led on track? thanks

  • What make and model are the new bulbs and the dimmer? – ThreePhaseEel Dec 31 '19 at 0:10
1

You're saying "last one", but that has two meanings. First as position: the last one in the row. Second as time: the last one remaining.

The second meaning is relevant here. What's actually the case is all 4 sockets are wired the same. What's causing the problem is removing the last (final) incandescent. It wouldn't matter if you removed it from position 2, 3, or 1. Once there are no incandescents left, the problem occurs.

The root problem is one we are familiar with here, and has many, many Q&A. The short answer is a bad dimmer, a bad choice of LEDs, or a combination of the two. For LED dimming to work, you need both dimmable LEDs and an LED friendly dimmer. Assuming you bought these LEDs prudently, it's time to look at the dimmer.