I have an older Slant Fin Liberty oil furnace that safeties out sometime around 4 hours. It seems to be intermittent because I have seen it do more than one cycle. The recent history on it is about a month ago I changed the electrodes, nozzle and filter. It was running fine until a couple of days ago. I noticed pressing the reset caused it to kick right back on and appear to run normally for several hours. What should I look for to troubleshoot this? We did get oil delivered. Maybe something with the fuel?

UPDATE 1:

I noticed this morning when I reset it, it fired then quit. I could hear the electrodes zapping. I had to reset it an addtional time after it quit. I'll pull the filter and check the flow later this morning.

UPDATE 2:

Added a video to demonstrate what I am dealing with. Please watch.

https://www.youtube.com/watch?v=P2T1W_llnz4

  • 1
    Hello, and welcome to Home Improvement. Could you add a picture of the furnace's wiring diagram? And, you should probably take our tour so you'll know how best to participate here. – Daniel Griscom Dec 24 '19 at 13:12
  • 1
    Did your fuel run dry? There should be a flashing light near the rest button, count the flashes and this will be the error code. What type of burner do you have? What is the name of the controller with the reset button /flashing light? – Gunner Dec 24 '19 at 14:17
  • 1
    You have air in the fuel/lines, you need to purge this air out of the system. Why is there air? Did you tighten the filter housing enough? Did you forget to remove old gasket so now there are 2? Is the bleeder screw on top of the filter tight and have a gasket? Are all fittings tight? The filter housing would be my first check. – Gunner Dec 24 '19 at 17:20
  • 1
    Can you try to tighten the fittings on the valve? No tape! If any gets loose and into system, it will screw up the pump and gun. Use something like Gasolia thread sealant. The valve you describe that works opposite of normal valves.... That is a special valve that is supposed to shutoff in high heat (a fire) – Gunner Dec 24 '19 at 20:49
1

I wanted to share the additional steps I took to troubleshoot the issue and describe what was ultimately causing the issue. The problem comes down to a weak and short spark. I was able to test the spark and witness that it was very quick and dim. I replaced the transformer and the protector relay. I likely did not have to replace the protector relay but figured it could not hurt. A retest with the new components showed a strong spark. Now I am back in business and should not have to worry about either of those components for years to come.

| improve this answer | |
  • 1
    Glad you were able to lick the problem in the end! – ThreePhaseEel Dec 27 '19 at 3:13
0

No tape! If any gets loose and into system, it will screw up the pump and gun. Use something like Gasolia thread sealant. The valve you describe that works opposite of normal valves.... That is a special valve that is supposed to shutoff in high heat (a fire)