I need to install a NEMA 14-30 outlet in my garage. It will be installed within 2 to 3 feet of the breaker box. My question is for esthetics. Can I run the wire from the bottom of the box through a pipe over the wall and install the box below the panel or do I need to run the wire up through the ceiling and then come down to install at a particular height? Where would you run the wire and install the outlet for a professional looking job?

Thanks in advance for your input.

UPDATE: Thanks for all the input. Ive decided to go with a NEMA 14-30 on a 30 amp breaker and 10/3 wire. Everything went well.enter image description here

  • Welcome to StackExchange! Wait. Is your desirable outlet location on the other side of this wall?? Which side of the wall are you concerned with aesthetics on, this side or the other side? – Harper - Reinstate Monica Nov 24 '19 at 17:36
  • I am adding the outlet to the right or left of the panel. I am thinking the most professional looking job would be have the wires going up to ceiling and then coming down thru a conduit down to the same height as the other regular outlets. But it would be easier just coming down from the bottom of the breaker panel. I am just wondering what would a professional electrician would do? Thx for your input. – Rickspfc75 Nov 25 '19 at 23:48
2

Conduit

Any wires below a certain height need to be protected. In a typical wood studs + drywall setup, that can be running the wires inside the wall, protected with metal plates in certain locations. However, with a block wall you will run the wires outside the wall, which means running the wires through conduit. Once you are using conduit, you can run the wires pretty much any way you want to, as the conduit protects the wires wherever they go. A few things to keep in mind:

  • You definitely want to use individual wires, not cable, as that will be much easier to push through conduit.
  • There are limits on how many turns in a section of conduit. That makes it easier to pull wires through, but is less of a concern with a very short run - but you do have to follow the rules.
  • If you are using this for an electric car charger, you may want to upsize for a future larger charger. The breaker and receptacle need to be sized to match each other and to match the specifications of the charger. The wire can be larger to support a larger charger in the future. On the other hand, since you will be using conduit, you can always replace the wires later relatively easily.
  • You may need GFCI protection. In this case (unlike 5-15 and 5-20), the breaker is the place to do it. As noted in comments by others, it looks like GFCI is a requirement in a garage only for < 150V - i.e., your typical 120V 15A and 20A receptacles but not required for 240V (dryer, car charger, etc.). (I'm not a professional, and I don't have a garage, so this isn't something I'm that familiar with.)
|improve this answer|||||
  • 3
    You can fit 4 THHN #10 AWG in 1/2" conduit but not 4 #6 AWG so use at least 3/4" EMT. – JACK Nov 24 '19 at 15:02
  • 1
    Since this will be in a garage it will have to be GFCI protected in the panel – JACK Nov 24 '19 at 15:05
  • 1
    @JACK And for a few feet, the cost difference between 1/2" and 3/4" is peanuts. – manassehkatz-Moving 2 Codidact Nov 24 '19 at 15:12
  • Could someone provide a reference for 240v needing gfci in a garage? – NoSparksPlease Nov 24 '19 at 15:36
  • @NoSparksPlease I commented on this due to the fact that it was in a garage. I could be mistaken. – JACK Nov 24 '19 at 15:45
1

You do not need to run the pipe up, then come down, there is no specific mounting height required. There are accessibility rules, and many appliances have instructions included with the appliance that prohibit using extension cords. The instructions are part of the UL listing.

A Professional looking job is subjective, extra bends in the conduit will be the biggest eye sore. Personally only a couple feet away I would just put a 90 out of the bottom corner and run straight to the outlet location, just at least far enough enough to not encroach on the 30" access area in front of the panel.

I don't understand that the NEC requires GFCI (or AFCI) for a 240v receptacle in a dwelling unit garage.

|improve this answer|||||
  • Any reason they couldn't come directly out the side, even? – ThreePhaseEel Nov 24 '19 at 18:00
  • You could come out the side, my hesitation is you have to drill a hole larger than the conduit to accommodate the fitting and any error at drilling through the furring would be more visible than drilling through the bottom. – NoSparksPlease Nov 24 '19 at 20:23
  • I do wonder if there's a furring piece at the bottom of this box as well... – ThreePhaseEel Nov 24 '19 at 21:15
0

I'd pick any mounting point for the receptacle that I pleased; however, I'd try to arrange it so the mounting point aligns with one of the knockouts on the panel, e.g. on its sides. It has many on its sides; for some strange reason someone framed around it, but I'd go right through it. Regardless, I'd connect with a 3/4" EMT conduit bent no more than needed; out the bottom I'd use an LB conduit body for a sharp turn, otherwise a pipe bend.

Then I would either put the mini-S-turns on the conduit so it runs flush against the wall, or just mount it to the wall with spacers every foot or so.

Paint the EMT and the box wall colors.

|improve this answer|||||