My home was built in 1941. The wiring is a mix of original and some added updates. I recently went to wire in a bath exhaust fan and timer switch on the same circuit as the light-switch (they share a box now) I traced the circuit (14) to a nearby box with a ceramic light also on circuit 14.

This small octagonal box had 8 cables coming out of it. Using a voltage tester I determined circuits 10 and 12 also ran through this box. With all 3 circuits turned off I proceeded to separate circuits 10 and 12 into different junction boxes to free up room to tap off 14 for power - and I prefer not to have multiple circuits in the same box for reasons I am about to come to.

The voltage tester indicated voltage was not present, but when I disconnected a group of white wires I saw sparking and lights I know to be on circuit 8 went flickered and went out. I turned off circuit 8 (that's now four breakers off to cut power to this one junction box with light).

After separating all the wires for 8, 10, and 12 (14 was wired to itself and not interconnected like the other 3) I turned the circuits back on and found that both the black and white wires from circuit 8 were 'hot'. There are 3 sets of 3 and 4-way controlled lights on 8, but no switch position checked had any effect on either black or white, they always stayed hot.

Tracing 8 I found that there is a cable going from one junction box back to the panel with the black removed completely (white and neutral only) and another that goes to another junction box down-line on circuit 12 (again white and neutral only with black removed completely from the sheathing).

This wiring has been this way for at minimum 22 years (my father may have added some of these wires between 1985 when they purchased the home, and 1997 when he passed, or the previous owners may have done this) Either way, in 22+ years it has been working, but I haven't a clue as to why it would have been done this way, nor if it's to code.

10 come from the panel to the box (what i thought was down-line circuit 10 is actually fed from a junction box on 8), 12 also comes from the panel, but has two cables feeding down-line.

Attached is a diagram showing the connections that concern me black of 10 to black of 8, white of 10 to white of 12 (not from panel), all 3 blacks of 12 are connected together, and the 'Hot' white from 8 is connected to the white on 12 coming from the panel as well as the white on the other 12 that runs down-line.

enter image description here

4
  • At the the time the home was built it wasn't uncommon for the entire house lighting and some outlets to be on one circuit. Is this not code today. at your wire court alone that would take a very large box. Today’s code requires a circuit for the bathroom by itself or possibly powering an adjacent bathroom. Since you did not mention where all the circuits go I just mentioned the basics. 2 circuits in one box is very common and almost every home I have wired has several multiwire branch circuits. What needs to be fixed is the neutrals need to be on the same cable with their hots from the panel
    – Ed Beal
    Commented Nov 18, 2019 at 1:51
  • Your labeling is a bit off -- is the wire you're labeling as "N" really a bare wire? Commented Nov 18, 2019 at 2:08
  • What is "N" and "W"? Commented Nov 18, 2019 at 3:01
  • Yes, the N is bare. Is neutral the white? I've only heard it refered to as 'common.'
    – 7monkeys
    Commented Nov 19, 2019 at 15:34

2 Answers 2

3

You're not supposed to disconnect wires with the power on. However, this can be a real problem in a promiscuous-neutral situation, where you don't realize another circuit is borrowing this circuit's neutral, thus putting current on it. It won't even show up with a voltage tester until you disconnect the neutral, and then whammo.

Don't let your guard down around neutral (or any other wire that's "supposed" to be safe); this is a good example of why.

White wires normally handle current

Current flows in loops. That's why everything has at least 2 wires. Current is flowing out the hot wire, to the appliances, then returning on the neutral wire. If you disconnect neutral, it'll spark because you are interrupting current.

Further, the disconnected side of the neutral will measure out as "hot", because electricity is trying to flow from hot via the appliance back to neutral, but it can't get back. It's normal in this case to read mains voltage across the neutral gap. (in fact, this "lighting up" of neutral is a huge reason ground is separate!)

Absolutely NO promiscuous neutrals

Your box's current wiring has neutrals sleeping with everybody. That's quick and lazy wiring, but it's very bad. Imagine you run three 20A circuits, that just happened to return all their current on the same neutral. That neutral will flow how much power? Anyone, anyone, Bueller? 60 amps, that is correct. Neutral wires don't have circuit breakers, so that's a huge problem. The neutral will set the house on fire and the breaker will never know.

There are ways to exploit split-phase or 3-phase geometry to intentionally share neutral wires (so that neutral handles only differential current), but you don't appear to be doing it here.

Currents must be equal in every cable or conduit

This is another rule that outlaws the promiscuous neutral. AC power kicks a heck of an electromagnetic field (EMF). When two adjacent wires have opposite flow, their EMFs cancel each other out. That's vital for safety - EMF causes eddy current heating, which starts fires, and vibration (which cracks copper and causes arc fires).

Imagine many ants running up and down branches of a tree. They never leap from branch to branch; they'll come down branch 1 and go up branch 2 rather than jumping. At the end of the day all ants go home. If you put ant turnstiles anywhere on the tree, you'd have exactly the same number of ants going out as coming back. Mains electrical is like that -- if you wire all your cables in tree/branch topology with each branch being 1 cable, currents will inherently be equal in all cables.

See how current is not equal in that 10-8-12 sequence. Current goes out the orange hot, but comes back on the red neutral via a different cable.

So... where hot goes, neutral follows. Always.

Now, with all that in mind, look at your drawing. Its hot (purple) serves two downline cables (OK so far) -- but it's neutral (red) serves two completely different downline cables (no, no, no!)

So pick and choose. For instance have green neutral go straight across to that cable orange hot serves. Then have red neutral serve the same cables that purple hot serves. This is mandatory and you should do it immediately.

When you have two disparate circuits in the same box, it's preferred to partition them. Or at least mark them with colored tape -- white and gray are allowable colors for neutral.

This may not solve all your problems, but at least this will be correct.

And to review: Hook up wires in order, and push them into the back of the box in order:

  • Safety Grounds (green, green-yellow and bare) first. They go in the back, you're unlikely to need to disturb them later, and this heads off a common problem where a device has a ground fault. If you hook up ground last, then it seems like ground is the problem when actually the device is defective. Hook grounds first. By the way, grounds are promiscuous - hook them all together along with pigtails to the steel box and to any devices which mount there.

  • Then Neutrals (white or gray)-- keeping diligent separation. I recommend marking, but use only white or gray, but don't go past middle gray, or it'll be confused as black on a switch loop.

  • Hots (every other color) on top.

5
  • The OP did say " With all 3 circuits turned off ", so he wasn't deliberately "disconnecting wires with the power on." Of course, it may be he meant "turned off at the wall switch", rather than "turned off at the breaker". Commented Nov 18, 2019 at 15:42
  • 2
    @MartinBonner Granted, that can be a problem in a "promiscuous neutral" situation because the entire point is that you don't realize the other circuit is poaching neutral. Commented Nov 18, 2019 at 17:15
  • Yes, the circuits were turned off at the breaker.
    – 7monkeys
    Commented Nov 19, 2019 at 15:55
  • @Harper-ReinstateMonica - Thanks for the detailed explanation. Having a basic understanding of house wiring, my terminology is probably off, B= black, W-White (heard referred to as common) and N is the bare ( heard called Neutral, but it would seem that is not accurate) This may be a situation where I am better to leave it to the professionals to remedy. I had a pro hook up my garage sub panel (lug box?) where black is on one buss and red on the other, and they share the white back to the main panel. Was told this was okay in that situation. Need I be concerned about that as well?
    – 7monkeys
    Commented Nov 19, 2019 at 16:05
  • You would be better to call white "neutral", and bare/green "safety ground". Neutral is an active conductor, hence the insulation and the sparking. You seem to be picking it up alright. Your sub-panel hookup is a situation I did describe, which exploits the characteristics of a split-phase system to intentionally hare neutral You can actually do that on individual branch circuits also, but it's definitely an advanced technique, and can't be retrofitted - it requres 4-wire (3+ground) cable. Commented Nov 19, 2019 at 16:37
1

Update, the problem has been resolved. I (at my wife's suggestion) took stock and mapped out all the switches and receptacles in the house and labeled which circuits they were on (which revealed a few other minor issues which are being corrected) This also allowed me to better trace the cables that feed the circuits in question.

As it turned out, there was a 3-wire cable with the neutral removed (black and ground only) supplying power to circuit 8. To remedy this, they pulled the black out of another 3 wire cable (white and ground only) and ran it over to a junction box on circuit 12 which led back to the original box I was concerned about (so far this is what my original diagram showed - though slightly mislabeled). Circuit 8 also had some wires running through conduit along with wires from circuit 10 and then split off two junction boxes later. The black was solid all the way through, but the neutral was joined together with the neutrals from 10 at this second junction box. I’m guessing this was original to the 1941 construction as they were twisted neatly and soldered together then wrapped with cloth tape.

To remedy this, I separated the two neutrals from 8 from the 3 neutrals from 10. Then I ran a new 12/2 with ground from the panel to circuit 8 to replace the black and ground wire. I ran a new cable from the panel to 10 as well as long as I was in there and eliminated the junction and cross wiring in the original junction box altogether. After that I removed the Neutral and ground wire from 8 to 12 to get all 3 circuits completely separated.

I did have an electrician come out to verify my plan before proceeding, he said I was on the right track, but he’s the one that found where 8 and 10 were tied together (I had thought it was in a different spot). They were running a special, so it only cost me $100 to have him out, but saved me some time, and the reassurance was worth it in my opinion. Thanks all for the advice.