2

In my garage I ran two separate 20 amp 120v lines, each to its own receptacle, each coming from one leg of my breaker box. I did this so I can run my table saw and dust collector at the same time. They are next to each other in the wall. I have a third unused 15A in the garage as well, where a refrigerator used to be.

I just received a free $1400 table saw that's 240v 12A. Am I able to make an adapter for the NEMA power cord (15A) that will split the 3 wires into two 120v plugs? For one plug, I will run a hot and a neutral and the other plug just the hot. This will give me 2 hots, one from each side of the breaker box, and a single neutral.

I know this isn't ideal, and ideally you would have a single breaker that would trip, killing both legs. But, if it did pull too much current from one leg, that would trip the overloaded breaker.

Please tell me how crazy I am. breaker panel

enter image description here

  • You can't do exactly as you're thinking, but you probably have some options. What's the wiring method here? Conduit, NM, or something else? And do the two circuits in question share a neutral (making it an MWBC)? A picture of your breaker panel would be helpful too. – Nate S. Nov 12 '19 at 0:21
  • This is an attached garage, so I just ran the two 12/2 wires through the wall into the garage. The big problem is I did this over 10 years ago, and a few years ago finished our basement with drywall on the walls and ceilings, including the room that has the breaker panel. I have no way of running new wiring out there, which would have been easy (maybe a small subpanel with then 240v and 120v off of it). It looks to be a single neutral. There's one "metallic" braided line coming into the panel, but two neutral "poles", one on each side. – Steve Warton Nov 12 '19 at 0:32
  • Well, that's a bit of a problem since you can't have the two hots be in two different cables for 240V use. How would you feel about converting one of your existing 120V-only circuits to instead be 240V-only? – Nate S. Nov 12 '19 at 0:41
  • Consider using your former fridge circuit for this -- you'd only need to swap the current 1 pole breaker for a 15A 2 pole, and swap the NEMA 5-15 receptacle with a NEMA 6-15, and mark the white wire with some colored tape on both ends -- perfectly standard, safe, and code legal. – Nate S. Nov 12 '19 at 0:44
  • 1
    Just how averse are you to having to rework some drywall? Also, can you post more detailed photos of your breaker box please? – ThreePhaseEel Nov 12 '19 at 1:09
5

Don't hokey-doke this thing when it's so easy to do it right.

You already have the right wires in the wall

You already have a dedicated circuit for your table saw. I presume you don't plan on running both saws at the same time. So we'll simply convert the dedicated table saw line to 240V and we're done.

Let's talk about the difference between a 240V circuit and a 120/240V circuit. A 240V circuit has 2 hots and a safety ground. A 120/240V circuit has 2 hots, neutral and a safety ground, and is able to power both 240V and 120V parts of the machine - such as a dryer's motor/timer or an oven's light.

A table saw will need 240V power. It has no use for neutral.

Convert the 120V saw circuit to 240V

The cable is converted from hot-neutral to hot-hot simply by marking the white wire with black tape to redesignate it a hot.

Now, it must be punched down onto a circuit breaker.

We could do some very difficult rearranging of panel space. However there's an easier way. There is a 20A 2-pole breaker in the left side center. We'll replace that with a 20/20 tied quadplex. Possibly a Siemens (ITE) Q22020CT2, which provides two tied 2-pole 20A breakers.

  • The inner breakers are tied and also are common-trip. I don't know what that existing 20A breaker serves, but it might need common trip. So we place that on the inner.
  • The outer breakers are tied, but do not guarantee common trip (they do promise common maintenance shutoff). They are suitable for this saw.

So for this saw circuit, remove the hot from the old saw breaker, and its partner former neutral (the one now marked with black tape). Both those go on the two (outer) hots on the new breaker.

By the way, whoever runted all your hots and neutrals to barely enough length to reach the breakers they're on now.... don't invite them back. Every hot and neutral should be long enough to reach every breaker space in the panel.

|improve this answer|||||
  • Harper, I REALLY appreciate you taking your free time to answer this and help me out. You made it very clear. Thanks! Also, so I don't have to go downstairs and rip the cover off and take a breaker out, is that the exact quadplex I need for my box? Thanks again! – Steve Warton Nov 12 '19 at 4:32
  • @SteveWarton your breaker box is a Siemens I take it? (the label on the inside of the door will say) – ThreePhaseEel Nov 12 '19 at 4:53
  • @SteveWarton ThreePhaseEel will know exactly what you need for sure, just put up the info off your panel door label (A photo will do). Mine was only a guess based on your breakers and ignoring CTL. – Harper - Reinstate Monica Nov 12 '19 at 15:54

Your Answer

By clicking “Post Your Answer”, you agree to our terms of service, privacy policy and cookie policy

Not the answer you're looking for? Browse other questions tagged or ask your own question.