In the process of installing a remote subpanel from my older backfed load center. The neutral/ground bar is attached to the service entrance via the screw midway, and the ground is at the base of the bar. This is an atypical bar in comparison to the newer panels I have worked with. Each terminal is part of a single sliding rail.

What would be the best way to attach a neutral lug capable of handling #3AWG for a 100a subpanel?

Also I understand that per code I should rearrange the neutrals so each occupies a single terminal.

enter image description here

Possible solution

What problems could I run into by simply doing the above? The lug is rated for 100a and would provide a direct path to the service neutral.

enter image description here

With a little bit of effort, I was able to get the #3 copper into one of the lower lugs. Any reason this might fail inspection?

12
  • Can you post photos of the labeling on this meter-main? – ThreePhaseEel Nov 2 '19 at 17:33
  • @ThreePhaseEel the only labeling on the box is the UL tag. Box labeling appears to have fallen off. – SaunaBuilder Nov 2 '19 at 20:49
  • Also, is there a reason you're using copper for this? – ThreePhaseEel Nov 2 '19 at 21:02
  • @ThreePhaseEel Copper is what was available locally – SaunaBuilder Nov 3 '19 at 1:42
  • That is strange that aluminum is unavailable locally -- are you sure you don't live in/near a jurisdiction that bans aluminum wire? – ThreePhaseEel Nov 3 '19 at 2:11