I just bought a dimmer switch from Lowe's, and it came with aluminum connection wires (I believe). Our house wiring is copper. I understand that connecting aluminum to copper isn't recommended, and requires some special connectors in order to be safe. I also have read that aluminum wiring in general isn't recommended anymore (for the last several decades).
So I'm trying to understand, why would Lutron sell dimmer switches with aluminum connecting wires, when most houses today have copper wiring, and connecting copper to aluminum causes special issues? The instructions that came with the dimmer say nothing about the copper-aluminum issue; they just say to use the (not special) wire nuts that came with the switch.
Similarly, this seemingly reputable article from FamilyHandyman.com shows a dimmer switch with apparently aluminum wiring, being connected directly to copper wiring, with no caveats. Strangely, it cautions "Also, if you have aluminum [house] wiring, don’t mess with it! Call in a licensed pro who is certified to work with it." They caution the user about aluminum house wiring, but show no concern about the wiring from the dimmer, which looks like aluminum.
So that makes me wonder ... are these wires on the dimmer actually not aluminum, even though it looks like it? Here's a photo I took:
wire end
I searched online for information on identifying wire, but what I found didn't really answer my question. Some articles online mentioned tinned copper, that looks like aluminum; but (a) it sounds like tinned copper hasn't been used since the 1960's or so; and (b) I see no sign of copper on the end of the wire (though I didn't try cutting it).
So to sum it up: If these wires are aluminum, why do Lutron and FamilyHandyman.com not say anything about connecting them to copper? If they're not aluminum, what are they, and how can I tell?
5 Answers 5
I would guess that that's tin, or some other solder alloy.
Coating copper in tin makes a surface that wont oxidize as much (or in the same way, I'm not sure). This is good when you're expecting to need a surface contact later.
You can tell if that's what you're seeing, by snipping the end off with some (sharp) clippers. If the cut is clean, you should be able to see whatever metal is in the middle. I don't know of any reason not to do this, but that doesn't mean you should.
This is tinned copper, for sure
Device pigtails, for flexibility reasons, are often made from a finer-stranded copper that is tinned to protect it from corrosion, and may have its ends soldered to allow it to be easily terminated into wirenuts and push-in type connectors. (While tinning wire ends is not a recommended practice due to fatigue issues, it can be made to work in a low-flex application such as building wiring; the proper practice would be to use a crimped-on wire ferrule to consolidate the strands, but that's a bit more expensive than tinning.)
You aren't quite right about aluminum. The problems which plagued aluminum are about small branch circuits, and terminations/splice methods that were made for copper only and hastily rubberstamped for aluminum without proper testing. These problems have been fixed in a feeding frenzy of overkill - a new termination rating (CO-ALR rather than Cu-Al), the old aluminum alloy (1350) being entirely banned and replaced by AA-8000, and voluntary shunning of aluminum on <=30A branch circuits.
(On the other hand, aluminum wire in heavy feeder, such as between a service and a panel, is perfectly fine, and this has never been in doubt. Quite often, the lugs are aluminum. It's a waste of money to use #3 copper for a long run to a 100A subpanel.)
No one. No one. Would use aluminum wire on a dimmer.
They certainly would, should, and do use stranded wire, however.
In small wire sizes like this, stranded guarantees copper. Aluminum wire at the #10-12 sizes are always solid core, and smaller sizes are not allowed. Further, these leads are likely #16-18.
One problem with stranded wire, especially in fine sizes, is it can get a serious case of the frizzies. The cure there is to tin the wires with tin/zinc-based solder so the strands stay together. Zinc plays well with copper.
I called Lutron, and their answer was as follows. It's not aluminum; they don't use aluminum wiring on their switches. They were a bit puzzled by my description of the wire, but said the silvery color may be the solder used to solder the stranded wire together.
I asked, for future reference, how can I tell soldered copper wire from aluminum wire (since I can't see any copper color at all)? The technician on the phone said, you can't; but they don't use aluminum wire.
That is tinned copper and I see it in about one quarter of the switches I install. I usually cut off the tinning because of the stress on the wire. You can tell if it's tinned by stripping off more insulation... the tinning doesn't go that far into the insulation.