The original builder (USA, ca. 2006) ran exposed NM/romex between the fixtures. Maybe this is a nebulous question, but is that within code?
I had a similar situation when I replaced an under cabinet light. The entry point was a little different leaving a few inches of Romex exposed. I boxed it in with wood. I'll let someone with more experience answer. – Mattman944 Oct 12 '19 at 18:16
As an aside, I am replacing these old fixtures with similar but "linkable" led fixtures. The jumpers between fixtures are 3-wire/110V. I've read that exposed NM is not to code, on the other hand, these jumpers would seem just as non-compliant. – Electro-Bunny Oct 12 '19 at 20:19
Are these LED fixtures low-voltage, by chance? Low voltage is much more liberal... – Harper - Reinstate Monica Oct 12 '19 at 20:43
No, it is 110 coming into the fixture, whether it is hardwired, or linked from another fixture. – Electro-Bunny Oct 12 '19 at 21:32
You can look up NEC at NFPA.org- free registration required.
Comments in parens are my rewording.
334.10 Uses Permitted Type NM ('Romex')....shall be permitted in 1 and 2 family dwellings, and multifamily dwellings of types III, IV and V construction (and other buildings, but must be concealed)
A "For both exposed and concealed work in normally dry locations" (except buildings other than 1 and 2 family dwellings, and multifamily dwellings of types III, IV and V construction.)
334.15 Exposed Work
A To Follow Surface
Cable shall closely follow the surface of the building finish or of running boards
B Protection from Physical Damage
..."where necessary" (describes which types are acceptable)
Which means if the electrical inspector thinks the wire is exposed to physical damage.
So bottom line, this is "exposed" but "closely follow(s) the surface of the building finish" and doesn't seem "exposed" to significant physical damage, unless the inspector thinks so so it is code compliant if not elegant.
It seems unlikely the residents will poke sharp objects up there.
Article 320 is 'Armored Cable' Type AC, which says, "320.10...shall be permitted...in both exposed and concealed installations"
"320.12 ...Type AC cable shall **not be used...where subject to physical damage**"
In this situation, AC is allowed exactly the same way as NM in a 1-2 family house, which I'm assuming is the situation..
For the LED jumpers, you'd have to look at what kind of wire they are.
With 120vac the cable needs to be protected so no this would not meet current code. If you swapped the romex out for MC type cable it would or ok.
Code requires NM wiring to be covered by a minimum of 1/2” drywall or plywood. If closer than 1-1/4 inch to the surface a nail plate is required. The easiest way to run exposed wire in this case is MC or metal clad--it is a flexible metal covering that can be surface mounted. There is always conduit but that will be thicker and harder to install than MC.