I have a challenger panel with a burned bus and bad breakers. I'm looking to replace them. I called my local shops and they said they don't carry this anymore. Is there a replacement option without going to remove the entire box? I am mainly looking to replace the interior components Bus and breakers. I don't mind other brands as long as they fit. The panel is 100 amp and I have attached images of the label and the bus. Thank you.
What vintage is the panel and breakers? Have you gotten estimates for complete replacement?– Aloysius DefenestrateSep 21, 2019 at 16:35
1Can you give us close-up photos of the busbar damage?– ThreePhaseEelSep 21, 2019 at 16:40
Also, who do you have for an electric utility, and I take it this is mounted on the outside of your house, correct?– ThreePhaseEelSep 21, 2019 at 16:46
Specifically we need to see the bus damage under the lower 100A breaker (the upper 100A will not remove easily). The goal is to see how bad the bus damage is. You can't just strut into a shop and buy a new busbar; you'd have to be very lucky on eBay or find a specialist used-panel trader. The buses being nearly unobtanium, I'm hoping to save the bus. Challenger panels' buses are perfectly fine (other than damage done to them by failing breakers, obviously). The breakers are all bad, but there's a super easy fix for that.– Harper - Reinstate MonicaSep 21, 2019 at 19:32
A new panel's busbars won't fit because nobody makes panels that narrow anymore. Code now requires wire bending space (see that neutral) which is why all small panels died. I have a list of panels I can't replace because of this, including some 12 space FPEs barely 10"x12".– Harper - Reinstate MonicaSep 21, 2019 at 19:44
Haven't heard back from you, so here goes.
About the panel/breakers
This thing you have is a meter-main with 12 breaker spaces. The main is "backfed" meaning the main breaker is just one of the breakers.
The Challenger breakers are known to be defective. And because of that, many electricians treat Challenger panels as if they're defective. They're not. There's nothing wrong with Challenger panels. The breaker problem can be very easily solved: Eaton "BR" breakers are cross-listed for it. Take a look at any BR breaker, it says
Type BR
Type C
Type C is for your panel. Ba da bing! That's easy.
By the way, if the home inspection report had said something about that and you said "meh, whatever", replacing those Challengers with BRs would have prevented this. So next time you see something like that on an inspection report...
About that bus
Your plan, as you have presented it, is to "just replace the bus" using a components supply chain that does not exist in real life. This brand has been out of production for 30 years. Compatible buses go in the trash every week, but nobody thinks to upcycle them onto eBay or Craigslist becuase they are obsolete and connecting with a buyer is extremely unlikely. There are companies that specialize in old Challenger panels, and you can try, but this is an odd duck even among Challenger.
So replacing this bus is not gonna happen.
As far as finding a modern bus that will fit, the problem is panels of this style are also obsolete: the very compact buses and gutters are now illegal due to "new" rules regarding wire bending radius (see that neutral wire for why).
So fuggedaboutit. You only have 2 options: Save this bus or replace the entire meter-main assembly. Chassis and all. I'll talk about saving this bus.
Saving the bus
The bus position containing the melted breaker (9-12) is permanently useless. So now we have two questions:
- Is the bus underneath the fried breaker intact enough to use the bus area below it? (Because the feeder wires will reach there).
- Is the bus underneath the main breaker intact enough to continue in service?
Either way, we are going to change all the Challenger breakers here for Eaton BR/C. The Eaton BR2100 ought to do the trick, at $40 each. Betcha didn't think you could get out of this for $100, did you? :)
If all busing is in good shape
In this case, we leave the main breaker at its position, and fit the feeder breaker in positions 13-16. The cable will reach. Easy peasy!
If the bus below space 9-12 is fried, but the main is OK
In this case, we leave the main breaker where it is. We move the feeder breaker to positions 5-8. Any remaining breakers go to positions 1-4; no breakers exist below the main. This will involve extending the feeder wires; pull new wires if they're short, otherwise extend them with insulated Polaris lug splices.
If the bus under the main is roached
In this case, you will need to remove the bus bars which come off the meter socket, and replace them with #3Cu XHHW wire. This will need to be physically protected where they come through the hole.
The main breaker is then moved to spaces 13-16 (below the melted breaker), and it will need to be bolted down the same way it's bolted down now. The feeder breaker is moved to spaces 17-20. That leaves spaces 21-22 for anything that is now above the main breaker. Remember this panel permits "BR/C" duplex or quadplex breakers, which you can put in spaces 21-24.
I have replaced a couple of these. The back plane is narrower than today’s panels (code required space). The one good thing I have found in all but 1 case was that there were boards on the inside the of the studs to make the panel fit 16 on center. This means I was able to rip the spacer boards out and a new panel fit in between the studs. Just a note to help and save $ on this upgrade I have found raco (Hubble) brand “insiders” the best clamp / bushing to save time and $ with remodels. (I have no connection or interest in Hubble/raco other than I love this product) on top of going with a modern panel I would get one with more spaces, this can make the retrofit easier by itself and I almost always suggest a service upgrade (get a 150 or 200 amp panel) it’s only a few $ more. I have never been asked to downsize a panel but have been asked to upsize the same home 3 times. If they went with my original suggestion they would have saved thousands and several days less without power.
