Goal I'm attempting to accomplish: Create a blanket of globe lights that all hang at different heights such that the wires that the bulbs hang from are thin enough not to be too visible.

120V, 15A circuit. Plug a patio light stringer into that circuit and you've reduced the size of the copper from 14/2 to 18/2.

Now, let's say you were able to convert each socket on the patio stringer into a bunch of tiny outlets. Then from those little sockets, you plugged in another pair of wires leading to the bulb itself. You've basically created another small circuit, where the 18/2 stringer becomes the "main" feeding the little sockets.

To each socket, you wire up a 7 Watt C9 E17 G50 globe light.

Question: How small can the gauge be on the wire that leads from the "socket" to the bulb base to bring power to the bulb?Illustration

2
  • Welcome to Stack Exchange. You will have to provide more details such as the total length of your 18-2 lamp cord and the total number of the 7W bulb branches you will have off that lamp cord. – Michael Karas Sep 13 '19 at 8:49
  • 1
    Are you comfortable with the fixture becoming a fire-starter if anything goes wrong? – Harper - Reinstate Monica Sep 13 '19 at 9:04
4

Building wiring must be breaker protected

The first rule is that wire gauge must be sufficient to prevent wire overheating, in all conditions including fault conditions. So as far as any permanently installed, in-wall wiring goes, 20+A = 10 AWG wire. 15+ amps = 12 AWG wire. 0-15 amps = 14 AWG wire. You're not allowed to go smaller in in-wall-wiring. Also, lighting must be derated 125%, so a 13A lighting circuit gets derated to 16.25A necessitating #12 wire.

And the circuit must be protected by breakers of appropriate sizes. The only exception is the tap rules, which do in fact allow for luminaires, but don't allow smaller than #14 wire.

Mains wiring inside fixtures is also limited

Now, with 120V mains wiring, there's a bottom limit on inside-fixture wiring of 18 AWG. That is the smallest wire size you'll see allowed. So your 24 AWG tendrils down to individual lamps are a no-go.

Further, your plan is to fit C9/E17 sockets there. It is inevitable that some "epsilon minus" type will stick 40 watt incandescents in there. You must design your fixture for that, or, use socket types which prevent this, or don't use sockets at all. Which segues into...

Low voltage lighting is far less limited

If you want to dodge these design regulations, that's the way to go. Obviously you will not be using incandescent lighting on low voltage DC, because the voltage drop will require thick wires. But that means LED, and LEDs in low voltage configuration are so reliable they don't need sockets, which also solves the abovementioned "you must plan for idiots" problem.

So for instance you might build your horizontal festoon with something like C7/E9 sockets, or whatever... Then have tiny tendrils with a socket on one end, and a self-contained, hardwired LEDs+resistors on the other end. Given that you want 7W light, that's about 1W of LED light, so 80ma on that tendril @12V or 40ma @24V.

Your festoon, on the other hand, would need to be appropriately thick to avoid voltage drop, since 12V is very, very sensitive to voltage drop. It really depends on how many lights you have. For the festoon, you could simply use a pre-made string of Christmas lights with the normal bulbs removed, and attached to 12V or 24V.

1

Voltage times current equals power. Voltage = 120, power = 7, current = 0.06 amperes.

According to stayonline.com, 18 gauge wire longer than 50 feet should be limited to a current of 7 amps continuous. With the calculated current draw, you'd approach the maximum safe capacity at about 100 lamps.

If your installation permits, consider to use heavier gauge wire as feeders. A tree or grid type of structure with the main branches using heavier wire will improve the safety factor.

1
  • NEC 725.43 & 430.72 both limit 18 gauge to 7 amps. With this said in the U.S. the breakers are usually 15 & 20 amp for 120v circuits. If something goes wrong like a lamp failure your wiring could start a fire. – Ed Beal Sep 13 '19 at 13:40