hot tub gone but subpanel still being fed from main that has a 50 amp double. Can I run two 20 amp outdoor receptacles from that 50 amp subpanel?

  • 2
    Can you post photos of the inside of said subpanel? What are you trying to power with these receptacles, for that matter? – ThreePhaseEel Sep 7 at 17:27
1

If the subpanel was installed correctly You can run the two twenty amp circuits. They will have to be GFCI protected.

  • 1
    Many hot tub panels are wired for 240V only... – ThreePhaseEel Sep 7 at 18:09
  • 1
    So if the panel is 4 wire connected it would be ok. Since there is 1 outlet it should be ok or the existing outlet is not code compliant. – Ed Beal Sep 7 at 22:08