hot tub gone but subpanel still being fed from main that has a 50 amp double. Can I run two 20 amp outdoor receptacles from that 50 amp subpanel?
    Can you post photos of the inside of said subpanel? What are you trying to power with these receptacles, for that matter? – ThreePhaseEel Sep 7 '19 at 17:27
If the subpanel was installed correctly You can run the two twenty amp circuits. They will have to be GFCI protected.
| improve this answer | |
    Many hot tub panels are wired for 240V only... – ThreePhaseEel Sep 7 '19 at 18:09
    So if the panel is 4 wire connected it would be ok. Since there is 1 outlet it should be ok or the existing outlet is not code compliant. – Ed Beal Sep 7 '19 at 22:08