My apartment had an electric range which plugged into NEMA 10-30P/10-50P and was served by two 50A circuits. I will be installing electric/220V induction cooktop using the same circuits. plug breakers

There are three wires in the plug (red, black and white). inside plug

There are three wires in the new cooktop (red, black and green). plug

Instructions say to connect the green wire from the cooktop to the white wire from the wall. So far so good, except the outlet will need to be removed and some sort of extension box will need to be put in its place to allow the connection in the back of the cabinet.

Is it possible instead to put a plug at the end of the cooktop 3-wire cable? If yes, then is there an advantage to doing that rather than hardwiring it?

Electrical requirements for new cooktop: 3-wire or 4-wire single phase 208 or 240 volt AC, 60-Hz, on dedicated double pole circuit breaker of at least 40 amps.

For the old range: "You must use a single-phase, 120/208 VAC or 120/240 VAC, 60 hertz electrical system. ... connected to an individual, properly grounded, 40 amp (minimum) branch circuit"

I'm in NYC if that matters.

Here is my attempt at picture of the top of the J box behind the plug: top of box

And here is the sub-panel showing the three wires in question:

sub-panel

  • btw new cooktop says that if wiring to 4-wire then to leave white wire from power supply capped off as it's unused. – Asya Kamsky Aug 17 at 16:51
  • Is that 50A breaker in your main panel (where the main breaker is), or in a subpanel? Also, can you post a closeup of where the wires to the range outlet enter the outlet box? – ThreePhaseEel Aug 17 at 17:10
  • 1
    Also, 3" sounds like an illogically large diameter for the flex whip -- I'm thinking it's either 1/2" or 3/4" – ThreePhaseEel Aug 17 at 19:37
  • 2
    These facts: a) you're in NYC b) in a large commercial complex c) surely well inspected d) metal boxes with what looks like AC (not MC) cable, and e) no ground wires in the entire place, yet grounds test good -- combine to be a very strong signal that grounding is present at boxes via AC cables or conduits. My facilities are the same way, no ground wires in 4 buildings. – Harper Aug 17 at 19:38
  • 1
    Sorry was measuring circumference! Looks like 3/4. – Asya Kamsky Aug 17 at 19:40
7

In NYC, you will have 208V power. It's 3-phase, but that won't be an issue.

Grounding path

Through discussion, we've determined fairly conclusively that a) this complex's wiring is grounded, and b) the grounding is via conduit or AC cable jackets, NOT individually run ground wires. OP reports that his "sub?" Panel has no ground wires at all, yet grounds check out on receptacles, so that indicates boxes are grounded and ground wires are not run (except inside AC cable). That's not weird; I manage 11 buildings and all of them are that way. I don't even stock ground wire.

You need to make sure that the wires from the wall are #8 or larger. (The paper padding makes it AC cable, whose internal wires are THHN, allowing the 75C column to be used for 50A).

If hardwiring

You need to connect the cooktop's green wire to the box*. The white wire in the box needs to be capped off.

However, there's a snag with hard-wiring. You can't just glorp the wires down "wherever". You need to have the wire-whip enter the box correctly, and that means through a knockout. That knockout needs to be on the face of the box, obviously, so you need a blank junction box cover that has a knockout on its face.

Easy enough, but you don't have a standard box. Your box presents the receptacle mounting screws for 2 abreast (e.g a 2-gang box) and lacks the corner screws that standard 4x4 box covers use.

So, you'll want to head to the best electrical supply in the city (goes without saying, that ain't a big-box store) and find the rare steel blank cover plate that attaches to the receptacle screws of a 2-gang. Ideally this will have a 1/2" or 3/4" trade size knockout on it, but if it doesn't, the shop may cheerfully punch it for you.

1/2" trade size actually uses a 7/8" knockout.
3/4" trade size uses a 1-1/8" knockout.

Cord-and-plug connection

Make sure the cooktop allows this before you commit.

If you want to cord-and-plug connect this, you need to change the receptacle. That thing is an obsolete, dangerous NEMA 10-50, and must be changed for this application because you need ground and NEMA 10 doesn't have it.

Fit a NEMA 14-50 receptacle. This has 4 wires. Fit the white wire to the neutral pin even though this cooktop doesn't use it.

On the cooktop, you'll be replacing the entire whip with a cord, not putting a plug on the end of the whip (which isn't structurally equipped for that). Buy a 14-50 cord, and attach to the cooktop's terminal block. Neutral gets wrapped with tape, not tied to ground!


* The box has a hole in the back tapped #10-32, it's a bit smaller than the other holes. This takes a #10-32 screw, and they even sell green ground screws just for this. This needs a #10 solid pigtail, which is tied to your oven's green wire. DON'T just clump this together with the white wire "just in case", that would create redundant neutral-ground bonds, which can cause all sorts of trouble. Also do not use the pre-made ground pigtails sold at the store, as those will be #14 or #12 and you need #10. You can buy 1 foot of bare #10 wire cheap.

  • I don’t have an oven. Replacing range with induction cooktop only. – Asya Kamsky Aug 17 at 19:12
  • @AsyaKamsky Edited but that doesn't change any of my answer. – Harper Aug 17 at 19:15
  • It sounds like it’s key to find out if box is viable ground and I wouldn’t trust apartment management to know. Is there a way I can test that? – Asya Kamsky Aug 17 at 19:15
  • Also I’m now inclined to hardwire since I wouldn’t be able to utilize the existing plug anyway. – Asya Kamsky Aug 17 at 19:16
  • 2
    Stick with hard wiring it. I've put six of these in and none of them had a terminal board where you could remove the whip and install a cord and plug. All the wires were crimped to the whip. – JACK Aug 17 at 22:55
4

Yeah, that's BX/AC, so ground to the box

Looking at your closeup shot, I can tell that between the fact that the cable armor is stopped by the fitting (instead of a cable jacket, which will poke out into the box through the cable clamp as a general rule), the lack of a ground wire entering the box (which rules out type MC), and the individual paper wraps around the conductors seen protruding into the box (which is characteristic of AC/BX), this circuit, like the rest of your apartment, was wired using type AC (BX) cable, with the armor as the ground path.

You'll need to hardwire this, using a fitting and a faceplate

Since your cooktop comes with a flex whip and not a cord (or a place for a cord to go), you'll need to hardwire the flex whip to the box. You'll need a 1/2" flex/MC fitting (the straight vs. 45° vs 90° decision depends on what keeps the whip from trying to bend too tightly, although 90° would be a common choice here) and a 4 11/16" flat faceplate with a 1/2" KO in it for this. The green wire from the cooktop gets landed on a 10-32 ground screw in the back of the box, the hots from the cooktop connect to the corresponding hot wires in the box with appropriate wirenuts, and another wirenut is used to cap off the neutral wire from the wall by itself, as it's not used in this configuration. You'll need to attach the fitting and faceplate to the flex whip before you connect the flex whip to the circuit, by the way.

  • yep, I had a box of the right size to put on top of existing one and use a straight fitting (out the side) but that made it protrude into the cabinet too much and nearly touch the bottom drawer, so I found a cover with KO and a 90° fitting. Works beautifully! – Asya Kamsky Aug 18 at 0:12
0

Ensure that you know which of the 3 wires are your neutral of your existing 50 amp outlet ... In your top picture, of the 3 slots you see, the one on the BOTTOM is where that white wire should be connected to NOW.. That wire will be the one that will connect to the Green one on your flexible metal connection coming out of your induction cooktop. The other two are exchangeable..

Your cooktop is 30 amps, and that 50 amp breaker in your panels needs to be reduced to a 30 amp/ 2,pole. No need to change the wire out, your good there.

At your range plug, if there's room for an extension box which would sit atop your existing wall box, you COULD wire your cooktop to that.

  • I'm am unsure that you could put a "plug" on flexible metal conduit... I'd say NO unless there is a plug made for that. In either case, if there is such a plug made, it will have to be 30 amps, and SO WILL your wall outlet.. just like your breaker will be 30 amps... Just like your new induction oven... – Retired Electrician Aug 17 at 17:10
  • My cooktop isn’t 30A is it? It says it requires minimum 40A breaker. – Asya Kamsky Aug 17 at 17:10
  • I’m curious where the 30A came from - is it because that plug can be either 30A or 50A? – Asya Kamsky Aug 17 at 17:15
  • My bad, though it said 30. Replace that 50 amp breaker with a 40 then. There's another way to connect to that existing box after you remove the plug and cover. Your box is either a 4x4 ( 4 square box ) or it's a 4-11/16 box. In either case, take out the old plug and cover, get a "blank" cover and drill a 1/2" conduit hole in it...right in the center of it. Or if you can buy a cover with a 1/2" hole in it. Also buy a 90° flexible conduit connector and attach that to your flexible conduit on your induction oven.... – Retired Electrician Aug 17 at 18:19
  • It’s 4 11/16th box. Is there advantage to wiring a plug - if not I’m inclined to go with hardwiring as instructions recommend. – Asya Kamsky Aug 17 at 18:33