Amp ratings: derate, add, and compare
The 0.14A rating (or VA divided by your line voltage) indicates the maximum amps it might draw.
Since the device is a light, you must increase this number by 125%, so you are now at 0.175A.
You must make similar calculations on all other hardwired loads on the circuit, increasing by 125% if they are continuous loads or certain statutory items which must be treated as continuous loads.
Add them all together, they cannot exceed the breaker rating. (15A)
If the hardwired loads add up to more than 50% of breaker rating, there cannot be any receptacles on the circuit.
Box fill
Based on the stated cubic inches (9.2), the box can hold four #12 or #14 wires.
The labeling is saying they got an exception from UL allowing six #14 wires, since five is pretty useless.