I am wiring up my unfinished basement for rough-in inspection. My understanding is that to wire 30 recessed lights (9w each), I can wire with regular 14/2, in the image below. enter image description here
However, my PS Knight code book shows me a diagram with a 3 wire cable between fixtures. Is this necessary? enter image description here
  • This is only to 1 switch, as seen in the diagram. – Will Aug 3 '19 at 1:39
  • i think that the second picture should show more of the page – jsotola Aug 3 '19 at 1:41
    30 is a large numer of lamps have you considered using low voltage lamps? – Jasen Aug 3 '19 at 2:35
  • Hi Jasen, they are all 9 watt recessed lights, so it comes out to 270 watts on a 15amp/120v breaker. That should be more than acceptable no? – Will Aug 3 '19 at 12:17
You only need three wire between the fixtures if the switch is on a branch off from the lamps
supply =2+e= lamp =3+e= lamp =2+e= switch
but new requirements for smart switches require 3 wires to the switch in that setup now
supply =2+e= lamp =3+e= lamp =3+e= switch
That setup is frowned upon these days because CFLs can blink when the switch is off.
You have the supply going direct to the switch (which is the preferred setup) so you only need 2+earth going from the switch to the lamps
If any of those boxes are metal the earth wire should connect to the box. if not just join it with a wire nut as you show.
| improve this answer | |
    That setup is fine, and is electrically equivalent to what OP is doing -- but hold on, the last lamp-switch wire must use 3+earth, because you must bring actual neutral to the switch along with hot and switched-hot, to keep people from bootlegging neutral for smart switches. That has been a requirement since 2011 in the US. – Harper - Reinstate Monica Aug 3 '19 at 3:56
The book is describing a situation where the power is left of the lamps, and the switch is to the right. Further, the book is wrong - you must use 3+ground cable between lamp and last switch.
Or to be more precise:
  • Neutral (white) must go to every location including the switch.
  • Always-hot (black) must go between the power source and the switch, no matter how far that is.
  • Switched-hot (red or other distinguishing color) must go between the switch and all lamps. If black is not needed in this particular cable segment, then don't use 3+ground, use 2+ground and mark the black wire red (for real or pretend).
Since the switch is the first place power goes, you don't need always-hot between switch and lamps, so 2+ground cable is appropriate throughout.
I've been staring at this for sometime now trying to think of why you would need 3 wire cable between fixtures and can not come up with a valid reason. I'm thinking it's a typo and should be 2 wire cable as it is from the panel and to the switch.