One zone of my sprinkler system comes on at times and not at other times. We have 70 PSI at the meter coming to the house which drops to 20 PSI when the zone comes on. If the heads come up, the pressure rises quickly to 35-40 PSI. If the heasd just gurgle and squirt, then the pressure remains at 20 PSI. We have had the backflow checked as well as the water meter replaced. I don't know where to turn as they come on sometimes and not others. Any ideas what would be causing this?
If your zone valve had a problem then the pressure at the meter would not drop. Any chance that there is a break in the underground pipe, maybe a tree root, that's causing the drop in pressure and the lack of water through the sprinklers? How long does that zone operate?– JACKCommented Jul 27, 2019 at 17:53
The zone operates for 30 minutes. I thought of a break but can't figure out why they then operate some of the time and not others.– JerryCommented Jul 27, 2019 at 18:23
A tree root causing partial leakage?? Have you walked the route after 30 minutes of the zone not working and checked for a really wet location?– JACKCommented Jul 27, 2019 at 18:30
Reason
A sprinkler head's pop-up mechanism seals and becomes water tight when fully raised/extended. This only happens after being supplied with sufficient water.
A sprinkler that is not fully extended will allow more water to exit than the same sprinkler that is fully extended. The high water pressure actually creates its own water tight seal, and only allows water to escape through the spray head. Low pressure water will escape from around the pop-up mechanism and the spray head.
The catch-22 is that with too low of pressure, the system can't self seal and build up pressure. It will do what you're seeing and just continue to never seal.
A way to test that I'm correct is to get a small group of people and have one person stand over each sprinkler head and pull it up while the system is showing these symptoms. Fully extending all of the sprinklers manually and holding them there will seal the system and make it start working on it's own. They could all now walk away and the system will continue to work until it is shut off.
After my explanation, it may seem like I'm saying that your problem is low pressure. Your problem is actually low flow. Water pressure only exists because of a restriction to flow. If you cut off the end of your water main after your water meter and let the water freely shoot towards the sky, you'd have 10 gallons per minute of water going everywhere, but your water pressure would actually be at 0 psi. Water pressure doesn't mean much without knowing the amount of flow as well.
It's confusing because your sprinklers seal from both flow and pressure in a way. They seal when the restriction to flow is great enough to raise the heads and make them stay there. If you don't have enough flow, you'll never build up enough pressure to overcome the leaks around the pop-up mechanism for it to self seal.
If we can increase the flow at startup to this zone, it will make the sprinklers seal. Or if we can decrease the number of sprinkler heads on this zone, we can reduce the flow required to make the the sprinklers seal.
Solution
The solution requires you to find out why this one zone is different from the others. Does this zone have more sprinkler heads than the others? Reduce the number of sprinklers on that zone.
Is this zone at the end of a long run of a copper pipe that's too small of diameter, or a galvanized steel pipe that's corroded and restricts flow inside? Install a larger diameter pipe from your main to your valve.
Is your sprinkler solenoid valve only 3/4"? Increasing it to 1" might be all you need to do. The sprinkler solenoid valve is typically the largest bottleneck in the entire system.
Splitting your misbehaving zone into two zones is an option, as that will cut the flow required to self seal in half.
If you can't do anything significant like that, your final option is to replace your sprinklers with low flow sprinklers with the same coverage. You'll need to water for a longer duration, but it'll reduce the flow required to self seal the system at startup.
Conclusion
Anything that will increase flow to this zone and removes bottlenecks, or that reduces the amount of sprinkler heads or the sprinkler head flow will be how you fix this problem.
Dotes has given a good explanation. If the system used to work then perhaps one or more of the popups now is faulty. You can clean the filters of the popups, though that is unlikely to help this exact problem. For each popup you can lift it manually, unscrew the top, get a friend to take the filter out and clean it while you still grasp the tube. then re-assemble. Test. To find a bad popup, have friends hold down and seal half of them, and watch the behavior of the others. Then try the other half. My boss always replaces bad popups, I dont know what the chances of them working are if you just take them apart and clean them.