We have a dryer plug we no longer use. We would like to make it a quad outlet box instead. The outlet is wired to a fuse panel with 2 30 amp cartridge fuses. Is it within code to switch those 2 fuses to 20 amp fuses and then wire the existing wires to 2 separate outlets with a shared neutral. It is a 208 circuit currently which should make the shared neutral just fine, but I want to make sure. I also thought about putting 2 gfci outlets instead of regular ones so that if it does trip we can simply reset it, instead of having to replace a fuse.
Can you post a photo of the inside of the fuse panel please? Also, how large is the box for the existing dryer outlet?– ThreePhaseEelJul 24, 2019 at 23:32
No currently. It is a quad. 4”x4” box. I will when I get back home.– Pizzaguy321Jul 25, 2019 at 13:31
1I think we might have a code issue on this since you are changing the wiring, is your fuse block a double where both fuses get pulled ? Note a GFCI is not a circuit breaker it will not prevent overloads just ground faults. If your outlets will be in a garage or out buildings GFCI’s would be required. I know mwbc did not require handle ties years ago so it may have been legal but the books I have don’t go back far enough to be sure.– Ed BealJul 25, 2019 at 14:14
dropbox.com/s/fk5vmzodzxd6dco/IMG_6110.HEIC?dl=0– Pizzaguy321Jul 25, 2019 at 15:18
Can you post a zoomed-out photo of the inside of the switch, as well as a photo of the switch's label?– ThreePhaseEelJul 25, 2019 at 22:18
1 Answer
That's just a disconnect
That's not an old fuse-era fuse box. That's a perfectly modern shutoff switch/disconnect.
That guarantees it is fed from somewhere else. Somewhere else, there will be a service panel of some kind. The vast majority of service panels generally are circuit-breaker panels, (with equal chance of being modern, old or ancient). So there's good chance of it being a circuit breaker.
The breaker and fuses do the same thing, so their protection is redundant. Actually the fuses are worse because they are not common trip, which is helpful for 120/240V appliances like dryers and ranges.
You can then change the breaker to 20A, and completely ignore the fuses. This application doesn't require the fuses, and many don't, but many do require a disconnect switch. Could be the installer grabbed the first disconnect switch he found, or got bad advice, or the cheapest one happened to have fuses.
So go find the actual service panel/breaker that feeds this location.
GFCIs don't do overcurrent
Imagine you take $9000US of cash through TSA security at LAX. TSA will not warn you that it will be confiscated in Toronto, it isn't TSA's job to screen for that.
It sounds like you are thinking GFCI receptacles will trip instead of the fuse. Just for the record, they are looking at totally different things. The GFCI will cheerfully flow 50A or more as long as hot and neutral current are equal. It will not trip for overcurrent, not even a little, that is not what GFCIs do.
The GFCI will trip for as little as 0.008 amps of imbalance current, and the fuse won't care about that at all.
However, if the advice above works out for you, there will be a 15-20A breaker in series with the fuses. The breaker should trip before the fuse in most cases.
Yes I will tomorrow, sorry I am away from home again. Thank you for the gfci explanation that helps! This is a disconnect switch instead of a fuse panel then. There is a handle on the side to cut power to the dryer plug. Are you saying I would need to change out the 2 pole 30 amp breaker to make it legal? The disconnect is directly above the dryer plug, while the breaker is far away in the basement. Jul 26, 2019 at 0:05