2

]My mother live in an older house and has two regular light switches in bathroom. one for light and other for exhaust for the exhaust fan

enter image description here

I would like to add an GFCI outlet in place of one of the switches and move both switches to one side.

The parts Im thiking of using are: 15 Amp, 120/277 Volt, Decora Single-Pole / Single-Pole AC Combination Switch, Commercial Grade, Grounding, Side Wired - Brown

15 Amp, 125 Volt Dual Function AFCI/GFCI Receptacle, 20 Amp Feed-Through, Tamper-Resistant, Monochromatic, back and side wired, nylon wallplate/faceplate, screws and self-grounding clip included – Brown

I would like the light switch to be independent of the outlet and fan switch

Im thinking of connecting the Fan switch to the load of the outlet.

Using my diagram, can someone please tell me how to correctly wire all this together? ex Light switch= LH>7 and LL>5 etc.

enter image description here

any help is appreciated.

P.S. As this is an older house, Im pretty sure there is no ground wire and the gangbox is metal.

P.S.S here requested pictures of inside of box enter image description here enter image description here enter image description here

  • 3
    Are you sure there's a Neutral wire in the box? Just because a wire is white doesn't mean it's neutral. Pull the switches out and show us a pic of how they're wired. – brhans Jul 17 at 14:07
  • 1
    The first thing is easy: Don't use the GFCI LOAD terminals. The GFCI will come with warning tape across the "Load" terminals; leave it there -- 90% of your potential problems will come from trying to use it, and there's no earthly reason to use it. "I don't know where else to put the wires" -> we will educate you. – Harper Jul 17 at 14:07
  • 1
    @Harper, is it not common to protect an exhaust fan with GFCI? I know I've seen it done, but I have no idea if its "proper" or not. – JPhi1618 Jul 17 at 14:21
  • 1
    AFIK it only makes sense to GF protect a receptacle which will be used for appliances you can touch in normal use. I see no reason to go out of your way to GF protect a ceiling exhaust fan or ceiling lights. Our two bathrooms (1970 build) are protected by a GFCI breaker and are wired on one circuit. So far no GF trips from exhaust fans, but if it did happen, then we would lose all lights and receptacles (one in each bathroom). Who needs that on some busy morning? – Jim Stewart Jul 17 at 14:38
  • 1
    A lot of hair dryers have a GFCI in their plug. Do your wife's appliances have that? You would still want GFCI protection for any receptacle close to the sink and I think code requires it for any receptacle in the bathroom, but it's not necessary for the fan and overhead light. What is the location in the bathroom of this 2-gang box? Do you have a receptacle in the bathroom already? – Jim Stewart Jul 17 at 14:59