So I have a three switch box and one goes to a light/receptacle outlet on the wall. The other two go to my ceiling fan. When I read the wires out when they are switched off I get 0vac. When I turn on the switch circuit that I'm not reading with my meter, I get anywhere from 28-36vac, then I turn on the switch that I'm connected to with my meter I get 115vac. Why am I getting the 28-36vac on my meter when I'm flipping the other switch on and off? The wall receptacle does not have any effect on the voltage in the ceiling.

marked as duplicate by Harper electrical Jul 3 at 16:54

This question has been asked before and already has an answer. If those answers do not fully address your question, please ask a new question.

  • Which wires are you measuring between? – ThreePhaseEel Jul 1 at 22:42
  • Can you plug any sort of load into the circuit? A night-light would do (as long as it's turned on). Then test again. Let us know if that voltage goes away. – Harper Jul 2 at 3:07
  • Phantom voltage is what you need to look up. There are several questions about it. – JPhi1618 Jul 2 at 14:17
  • Thanks for the help, – user103422 Jul 2 at 20:31
  • 1
    Meter reading without a load are meaningless. You need at least a small load, e.g. 100 kilohm resistor across the meter probes, to get a useful reading. – DrMoishe Pippik Jul 3 at 0:11