1

I have a Lennox 2.5 ton a/c unit, model 13ACD-036-230-05, with a blown dual run capacitor (the run terminal for the compressor is burnt off the can, the fan and common terminals are still intact, fan still running).

I had the cap replaced a couple years ago when the fan quit working. I remember the 5/45 uf, 440 volt cap that was installed was close to the original cap that failed, but not exactly the same.

I ohm'd out the compressor and got 1.4 ohms S-C, 0.9 ohms R-C, 2.3 ohms S-R. These values seem possibly reasonable to me, but according to LennoxPros, "The resistance between start(S) to common(C) is typically three-to-five times higher than run to common winding..." but they didn't state what resistance is actually expected.

What is the original cap rating (uf and voltage) for this a/c unit and what are the normal compressor resistance measurements?

wiring diagram from inside the unit,  ref. C12

  • Look up a wiring diagram (or other documentation) to find the original values. – Tyson May 28 '19 at 0:55
  • I checked the wiring diagram inside the unit. All it has is a label "C-12 CAPACITOR - DUAL". Checking several parts sources online, I found a number of different caps referenced for this model, ranging 300 to 500 volts, 5/30 uf to 7.5/60 uf. – Eric Simpson May 28 '19 at 3:34
  • @Tyson, I extended my online search but only found the same diagram, an installation guide, and a 2 page marketing flyer, nothing with specs on the cap or compressor. Do you have access to more helpful info? The original cap lasted 7 years, this one lasted 4. How long would you expect a cap to last? – Eric Simpson May 28 '19 at 11:31
1

I went through the Lennox web site to find a "store" near me and found an actual Lennox service center. They confirmed the 5/45 uf 440v dual run capacitor was correct. They didn't have any specs on the compressor coil resistance.

The service center didn't have any caps in stock but I found one at a local electrical supply house for under $10. It can also be ordered from Home Depot online (not available in stores) for about the same price.

I checked the resistance from each compressor terminal to ground (29-30 meg ohm each), re-checked the coil resistances (no change), put in the new cap, and turned it on. I noticed the current draw is lower than expected (9.2A @ startup, 8.9A running @ 230V supply vs. 15.4A nameplate) but It's working fine so far.

| improve this answer | |

Your Answer

By clicking “Post Your Answer”, you agree to our terms of service, privacy policy and cookie policy

Not the answer you're looking for? Browse other questions tagged or ask your own question.