Is there any requirement that mandates a residential floor-installed electrical receptacle to be a GFCI type, when said location is in a dining area, NOT located in the bathroom, kitchen, laundry / NOT near water source? Thank you!
-
1GFCI receptacles are never, ever required. Never. Where GFCI protection is required, you are allowed to use a variety of methods to provide it, such as downstream feeding, deadfront, GFCI breaker, whole subpanel GFCI, you name it.– Harper - Reinstate MonicaCommented May 23, 2019 at 1:10
-
Great, Appreciate your answer!– H1991Commented May 23, 2019 at 17:00
1 Answer
No, this receptacle doesn't have to be GFCI protected
The primary clause that requires GFCI protection in residential kitchens only applies to kitchen countertop receptacles (there's also a GFCI requirement for dishwashers, but that's a different thing):
(6) Kitchens — where the receptacles are installed to serve the countertop surfaces
However, it does need to be installed correctly
The problem with a receptacle in the floor, though, is that putting a regular box and receptacle in the floor yields a hazardous installation (due to crud getting into the receptacle), and is prohibited by 314.27(B), which requires a listed floor box and matching faceplate be used instead:
(B) Floor Boxes. Boxes listed specifically for this application shall be used for receptacles located in the floor.
So, you need to make sure the box is listed and labeled as a floor box -- these will generally have a distinctive faceplate that has flip-open covers over the receptacles themselves.