I am looking to do a pass through in my kitchen, and I was looking to confirm in the basement if everything lined up nicely for the 5-6' header I was going to put in. I noticed that the wall (load bearing) is not actually over the basement posts and joist but about 1 foot away. Is this an okay / normal occurrence?

basementposts

  • If you add an opening in a bearing wall that isn't stacking with bearing below, you'll create point loads that aren't supported correctly. Additional joists would need to be added, preferably sized by someone who knows what they're doing. – Dotes May 14 at 19:24
4

Yes, it’s acceptable to have bearing walls NOT align vertically, provided: 1) the walls are less distance apart than the depth of the joists, or 2) the side that has the upper bearing wall rests on a considerably shorter span, 3) the load is accounted for in the design of the joists.

1) If the upper wall is slightly off center, the upper load will transfer at about a 45 degree angle vertically down through the joists.

2) Usually all the floor joists are the same size (and spacing) throughout the house. The size is based on the longest span, so the shorter spans are “over designed”. Therefore, if the upper load bearing wall rests on a set of joists that have have a much shorter span, it’s probably ok, as long as it’s not in the middle third of the span or the load is minor.

3) Often we’ll just calculate the loads and verify that the joists are not overloaded.

  • Thank you. Yea it seems they are about 1’ off on one side and another wall is about 2’ off. (Hallway walls) – repsak May 15 at 16:24
  • @repsak But are they load bearing walls? – Lee Sam May 15 at 16:36