I have an new Emerson thermostat and would like to connect a c wire so it always has power. I have an extra wire that's not being used, but I don't have a C wire terminal on my furnace. I'm wondering if I can use any of the unused terminals or if I can tap into one of the wires coming off of the 24v transformer.

enter image description here enter image description here enter image description here

2 Answers 2

1

The blue wire coming off of the transformer is what you want, but there might be a better place to tie into that. Look for any wires that are simply screwed to the metal chassis of the air handler. You can check with a continuity tester, but those chassis grounds are usually a connection for that other side of the transformer (the blue wire).

Looking at that schematic, I can see a few places where a wire terminates to "ground", but I don't necessarily see any terminals where the "C wire" would be conveniently exposed. Also, when you find a ground screw use a volt meter to make sure you get a good 24v there between the ground point and the red wire from the thermostat and/or transformer.

2
  • Lol I think I edited your answer instead of mine.
    – Joe Fala
    Commented Apr 4, 2019 at 17:51
  • The B terminal already has a green wire on it. Can I just add another wire to that terminal? It will be ok?
    – Karl
    Commented Apr 4, 2019 at 17:53
1

The B terminal should be you common wire. It looks like you have air conditioning, one wire goes to the Y terminal and the other is common. Often marked B for heat pump applications.

enter image description here

It's literally the same as the blue wire on the transformer as in JPhi1618 pointed out. Either spot will work the same. The B terminal is easier.

5
  • The B terminal already has a green wire on it. Can I just add another wire to that terminal? It will be ok?
    – Karl
    Commented Apr 4, 2019 at 17:56
  • Fixed the edit... I believe you about the B wire, but that notation on the schematic is saying to "See note 5" on the right side of the label. The 5 being under the O and the B terminal is coincidence.
    – JPhi1618
    Commented Apr 4, 2019 at 17:57
  • There is a rectangle box on the left above all the text that lists "B/C" as a notation for Common, so makes sense. Voltage and continuity test can confirm if there is and doubt. And @Karl, yes, two of the same size wires under that screw terminal is fine - typically one on each side. One wire being larger than the other can cause clamping issues on some terminals.
    – JPhi1618
    Commented Apr 4, 2019 at 18:05
  • You guys are awesome. I'll try the B terminal tonight and let you know. Thanks!
    – Karl
    Commented Apr 4, 2019 at 18:52
  • I finally got time to do this yesterday and it worked beautifully. Thanks again!
    – Karl
    Commented Apr 8, 2019 at 19:44