0

GE Cafe series C2S986

The maunfacturer's spec is 30 amps for oven. Want to replace existing range wire ( old 3 conductor for the mid '80's) on a 50 amp breaker. What size wire for this new 30 amp "oven" circuit would meet the current code?

2
  • To clarify, there's a 50A breaker there now, and you want to replace it (and the wire) with a 30A breaker?
    – mmathis
    Feb 22, 2019 at 13:31
  • Can you post a photo of the existing wiring box? Also, is running a new cable, or a separate ground wire, at all an option? Feb 22, 2019 at 23:48

2 Answers 2

1

You just need to change the breaker to protect the stove. You don't need to change the wire because you can oversize the wire.

0

To meet current code a 30 amp circuit would require a 10 gauge wire with 2 hots, 1neutral and a ground. I say this because a 30 amp circuit requires #10 wire. If the stove requires 30 amps then you would need to go up 1 size to 8 gauge , 2 hots, 1 neutral and a ground. When I installed a similar setup at my last home I left the larger wiring installed and just changed the breaker and outlet but this was 4 wire.

Your Answer

By clicking “Post Your Answer”, you agree to our terms of service and acknowledge you have read our privacy policy.

Not the answer you're looking for? Browse other questions tagged or ask your own question.