I have one 15 amp GFI breaker in my main panel. We have two patio outlets, the garbage disposal and one outlet in each of the two bathrooms all wired common. Whenever we have company and women are using hair dryers at the same in each bathroom the breaker trips. Would it be OK to replace the 15 amp breaker with a 20 amp so it doesn't trip anymore when they are drying their hair?

  • What size is the wire connected to the 15 amp breaker ? If 14Awg a 15 amp breaker is the max size. If 12 awg and all the wiring is 12 you could upsize to a 20 amp. – Ed Beal Feb 21 at 18:51
  • Thank you, I will check wiring. Kind of was thinking that in the back of my mind. – Edward Strife Feb 21 at 20:41
  • @EdwardStrife, you can look at the wire size, but it would be strange for the builder to to the expense and time (harder to work with) of using a thicker wire only to put a 15A breaker on it. – JPhi1618 Feb 21 at 21:16
  • 1
    Uphill I have done this in the past I normally wire everything with 12 and some special deals provided some breakers with the panels so I used the 15 breakers regularly on lighting circuits. – Ed Beal Feb 22 at 1:05
2

No! The goal of a breaker is to trip before the wiring starts a fire. If you increase the breaker limit without changing the wiring, the fire may start before the breaker trips. So, you would have to update wiring before you can think about changing that breaker.

  • It depends on the wire size, it is probably 14 gauge and your answer would be correct but if 12 gauge a 20 amp could be used. – Ed Beal Feb 21 at 18:53
2

A circuit is defined by its overcurrent protection (breaker) not the other way around. The circuit you are talking about was originally designed to be a 15A circuit not a 20A. What you really need to do is add two more 20A circuits, one for each bathroom. Here's why.

Your circuit trips while women are using hairdryers in 2 bathrooms. A standard hairdryer is rated 1500W on high. 1500W*2=3000W, 3000W/120V=25A, that is 5A higher than a 20A circuit breaker. So even if you were able to install a 20A breaker, there is a good chance you are still going to trip the breaker on that circuit.

You could do a few other things which might or might not be satisfactory, but in the end a substandard repair will render a substandard performance.

In conclusion do not change out a 15A breaker to a 20A without verifying that it is capable of being a 20A circuit. If for nothing else, it is against the law and might cause a shock or burn hazard. Sooner or later you are probably going to have to install two 20A circuits to each bathroom, so you might as well do it now. Then you will be done with it and it will be legal and most important the women will be happy.

Hope this helps and stay safe.

  • I certainly appreciate your advise,thank you very much. – Edward Strife Feb 21 at 20:46
1

You can never "just up-size a breaker to stop it from tripping". 15A and 20A breakers cost the same. If it was safe to use a larger breaker, the builder would have already done it.

It wouldn't matter anyway

A hair dryer, like most heat appliances, is 1500W because that is the UL limit for such devices. Two hair dryers are 3000W.

 The 15A circuit you have is rated for 1440W continuous or 1800W peak. 
 The 20A circuit you want is rated for 1920W continuous or 2400W peak. 

All of these numbers are well below 3000W. No receptacle circuit can support two heat appliances. That is a fact of life.

Upgrade the circuit

The only way to support dual hair dryers is with two circuits. With clever wiring in the right place, you can split the circuits into 2 or even 3 circuits.

Code currently requires that bathroom receptacle circuits serve no load outside a bathroom. It gives you two choices: one circuit can power receptacles only in any number of bathrooms (but you can see right now where that's a bad idea)... Or one circuit can power receptacles and other things only in one bathroom. That last one is the way to go. They need to be 20A circuits.

  • Well that really resolved the issue. Thank you very much, I guess the women will have to dry their hair at different times. – Edward Strife Feb 21 at 20:43
0

No, don't up-size the breaker. The breaker's job is to protect the wiring hidden inside the walls. The installer chose a 15 amp breaker because that was the code-approved rating to protect the specific wire used in that circuit. A higher-amperage breaker would put the wiring at risk of overheating and could lead to a fire.

There may be some other circuit near one of the bathrooms which could be extended to provide a new outlet in the bathroom. That would allow the hair tools to operate on different circuits. It would be necessary to add GFCI protection if this was to be done.

  • 1
    It depends on the wire size, it is probably 14 gauge and your answer would be correct but if 12 gauge a 20 amp could be used. I have seen homes wired in all 12 with 15 amp breakers. – Ed Beal Feb 21 at 18:54
  • Thank you for your expertise, it is very much appreciated. – Edward Strife Feb 21 at 20:49