Residential basement remodel problem:
Replacing old, ungrounded wiring. Problem is cinder block walls. Inside, the exterior walls have rigid insulation and one layer of 1 x 3 furring strips covered by drywall. Interior walls have simply drywall directly on cider block.
Aesthetically, I want to 'hide' all wires. There is no room for wires in the walls. We don't want surface raceway or conduit.
Can either armored or plain wires be run behind baseboards?
What if the baseboard is backed by 1/16" metal plating?
Also can armored cable be routed thru ceiling joists?
Or any other ideas and solutions welcome.
What will meet NEC? Thanks!
Is routing separate ground wires an option?– ThreePhaseEelFeb 3, 2019 at 13:34
Good thought on separate ground wire but all the wiring is dated so I am looking at an "all in" solution– user96616Feb 3, 2019 at 17:30
In "Wiring Simplified" 45th Ed. using 2017 NEC, page 157, Fig. 13-16, shows cable run in a groove behind baseboard and only protected by steel plate where the cable crossing a framing member; i.e. not in a full length U-channel as show below from fine home building. Can anyone clarify this?– user96616Feb 16, 2019 at 16:10
NEC 300.4(D) covers the type of installation indicated in the question, and it applies to both AC and MC armored cable. So you'll need to use a steel guard at least 1/16" thick to protect the cable.
This tip from Fine Homebuilding illustrates this type of installation. Rather than backing the molding with steel plating, they use a U-shaped channel to protect the cable, which should be much easier:
The illustration shows a nonmetallic cable and a plaster finished wall. You will need more depth than the thickness of the drywall to fit armored cable and steel U-channel. On your outside walls with the furring strip, you can just cut out the foam board with a knife and the furring strips with an oscillating tool to get the additional depth. On the interior walls, with the drywall directly on the block, I think you'll have to route a channel on the back of the base molding to make room. In fact it might be better to use that method on the outside walls, too.
You have another challenge here: getting the cable from the baseboard channel to the existing boxes. This might not be too difficult if you can fish the void in the blocks, but it could be a big can of worms.
Is there a special channel for this purpose and, if so, what is it called? Feb 3, 2019 at 13:08
@JimStewart - I'm afraid I don't know of any channel specifically made for this purpose. Feb 3, 2019 at 13:11
Thanks. Can I simply notch out the furring strips for the wire, place the wire, and then use steel plates to cover the notched parts of the furring strips? This seems like the same approved technique for 2 x 4's. And, same as Stewart, where can one purchase these steel U channels? Feb 3, 2019 at 17:24
When I looked at that picture, my first thought was, "What about a nail gun?" In other words, when the baseboard comes loose, how is someone to know that there's a wire behind it and to not just slap it with a cranked-up air nailer? Is the U-channel stout enough to protect against that?– AaronDFeb 4, 2019 at 4:01
You can retrofit just ground. Really.
The biggest misconception is that you must replace all the wires. Nope! NEC has allowed you to retrofit grounds on feeders and larger circuits for awhile, and it worked so well that in NEC 2014 they threw it open to all circuits.
This is an exception because ground is special. Normally, it's a fixed rule that currents must be equal in each cable or conduit. This is AC power and loops make inductors. This rule is enforced by a strict "tree" topology for cabling and conduit work, with no branch-branch crossovers. Retrofit grounds can follow any practical route, so that would seem to violate this rule. It doesn't, though, because the rule applies to active conductors - wires in which current normally flows. Ground only handles current during fault conditions.
It's possible your jurisdiction hasn't adopted NEC 2014 yet because it also requires GFCI and AFCI on almost every circuit, and that's widely seen a bit harsh. But these ground rules are something NEC has been building to for quite awhile, so they're not a surprise - and I doubt anyone would get written up for following the next codebook.
Read the ground retrofit rules, but the gist is that you can use any wiring route, no need to stay with the original route, and circuits can share grounds. The ground wire must be the appropriate width all the way back to the panel the circuit is served out of.
For instance, if you are trying to ground a 30A dryer circuit, you need #10 ground wire, so the #12 ground wire going to the washer is not enough. However, if you are grounding a 50A range, that also specifies a #10 ground, so it can share the #10 ground you just fit on the dryer.
So for any circuit, its ground can be run to any of several places:
- back to the panel
- to a junction box where there is another (large enough) ground wire going back to that panel
- directly onto one of the Grounding Electrode System wires, those thick bare wires that go from the panel to the ground rod or water pipe connection. You would tie on with a "split bolt".
- directly to another circuit's bare (retrofitted) ground wires, again via split bolt. You cannot cut into a cable to access its ground wire.
But I don't trust the old wires
The usual threat is arcing, which causes overheating and fire. That is a serious risk, but AFCI (Arc Fault) breakers are an effective solution.
You may already have ground, if you have metal conduit
Some houses are wired with individual wires in steel conduit. This will have metal junction boxes, and wire colors that match the wire's purpose - not always the black, white, (red) found in cables. These do not require separate ground wires, the steel conduit is the ground "wire". Believe me, I have put this to the test, and it works.
The only issue is that if you have a receptacle or lamp, it cannot rely on the yoke and mounting screws to carry ground current, unless the clean metal yoke bottoms out hard on a clean metal junction box. Typically the wall surface will be "proud" of the junction box, and when you tighten the screws, the drywall ears will hit the drywall before the yoke has bottomed. Stop there. That's what drywall ears are for. This means you will need a metal spacer to continue the ground, or most people just run a ground wire from the receptacle to the steel box. Most boxes have a hole in the back tapped #10-32 specifically for ground screws. They sell adorable litle green 10-32 screws just for this purpose, with or without pre-attached pigtails. (Any 10-32 machine screw will do). Don't use a self-tapping screw of your own, unless it is -32 or finer thread. It needs to be 6- or larger.
With metal conduit, if you are unhappy with the age of the wire, just pull it out and install new wire. You can use the old wire to pull the new wire. If the pull force is excessive, there's a junction box or access point in between: find it. It's illegal to drywall over access points, but sometimes people do.
I ran 14-2 under my baseboards in a gap between the bottom and the floors. I used the steel backing from 700 Wiremold raceway as the metal nail shield. Then covered the gap with shoe molding. Worked well as the Wiremold backing curves over the top and side of the wire, giving good protection. Tiny screws hold the nail shield in place. It is an expensive method as the top part of the raceway is rendered useless.