2

I want to replace and old Leviton attic light switch with a Leviton combo switch/outlet. The junction box has two Romex cables in and one out to the current light.

The two in have each a black wire going into to the push-in terminals of the switch and one black one connected to a side screw going to the light. Why would there be two romex cables with two black wires going into the switch? How would I install the combo switch with this wire config? The grounds are just wire nutted together (all three). Thanks for the help.

enter image description here enter image description here enter image description here

UPDATE: Here is a better shot of the back of the old switch with some labels: CORRECTION... New diagram here: enter image description here

enter image description here

enter image description here

Based on the updated diagram above... Romex 1 from bottom of box has the shepherd's hook and was attached to the screw... Romex 2 from bottom of box was pushed-in to the bottom of switch... Romex 3 goes to the light through the top of the box from the push-in connection at the top of the switch.

And here is the switch I'm needing to install:

https://www.homedepot.com/p/Leviton-15-Amp-Combination-Switch-Outlet-White-5225-WS/202077623?cm_mmc=Shopping%7CG%7CVF%7CD27E%7C27-2_WIRING_DEVICES%7CNA%7CPLA%7c71700000033102358%7c58700003867202208%7c92700031090651054&gclid=EAIaIQobChMI9taWn6eO4AIVQR-GCh1zkAC4EAQYAiABEgIIjvD_BwE&gclsrc=aw.ds

FINAL UPDATE... SUCCESS!!

Thanks to ThreePhaseEel (accepted answer) and Harper.

enter image description here

10
  • Can you post a better shot of the connections to the switch? Jan 27, 2019 at 14:10
  • Just posted a new photo of the back of the switch with some labels... Thanks again Jan 27, 2019 at 15:54
  • What does Romex 2 run off to? Jan 27, 2019 at 15:57
  • There are 2 Romex running into the bottom of the box... One black going to push-in terminal 1 and the other Romex black going into push-in terminal 2... The 3rd Romex is going to the light... You can see the 2 Romex at the bottom in the photo i.stack.imgur.com/mtwPZ.jpg Jan 27, 2019 at 16:16
  • 1
    Then Romex 1 must be the line connection, and Romex 2 leads off to something else that is being turned on and off by this switch...can you figure out where that leads? Jan 27, 2019 at 18:41

2 Answers 2

2

You're in luck!

The fact there are two cables here is a good thing, since it means neutral is available at this box. The wiring here goes as follows:

  • The always-hot black wires get nutted together and with a black pigtail of appropriate gauge -- this pigtail then goes to a black screw on the switch/receptacle combo
  • The switched-hot black wire goes to the brass screw on the switch half of the combo
  • The neutral bundle gets a white pigtail nutted in with it, which goes to the silver screw on the receptacle half of the combo
  • The ground bundle gets a bare or green pigtail nutted in with it, which goes to the green grounding screw on the device

Once it's all wired up, you can then button things up, turn the power back on, and enjoy your new receptacle!

If you want a switched receptacle

If you want the receptacle to be controlled by the switch, the wiring is actually no harder than an always-hot receptacle. Simply keep the neutral and ground wiring the same, but swap the always-hot and the switched hot so that the always-hot pigtail goes to the brass screw on the switch end and the switched hot goes to one of the black screws.

15
  • Is this describing a separate feed where the outlet is always on and the light switch controls the light independently? What if I want to have a common feed where the light switch controls the outlet? Jan 27, 2019 at 20:01
  • @mm-93 -- this is describing a separate feed. Why do you want a switched receptacle here? What are you planning to plug into it? Jan 27, 2019 at 20:03
  • Just an extension cord for extra lights where I need it in the attic... I’m running CAT6 cable... I just need an outlet to be available in the attic (instead of always running an extension cord from the garage) and don’t care if the switch operates it... in fact the switch will always be turned on when I go up there and turned off when I leave. Is it easier to wire a common feed? (I.e no pigtails needed?) Jan 27, 2019 at 20:25
  • The common feed is easier to wire -- you'd need to break the tab and use a pigtailed jumper if you wanted the outlet to be switched Jan 27, 2019 at 20:43
  • 1
    @mm-93 yes, you are correct Jan 29, 2019 at 1:18
2

Romex 1 and 2 are using backstabs, which is not a good idea for other reasons.

The backstab is simply connected to the screw nearest it, internal to the device. It's supposed to be an "either-or", but some people like to use it to splice the 2 wires together.

It would be the same as if the two wires were joined at a wire nut, with a pigtail from there to the device screw. That is exactly what you should change that to.

On a switch

One side is always-hot, and the other is switched hot to the lamp. There would be no reason to have 2 cables feeding switched-hot. Unless you had 2 lights.

It would be very common, however, to have multiple always-hot wires in a box; the second one would be going onward to other loads.

The grounds are nutted together ordinarily. The neutrals likewise, you may be adding a wire to this neutral bundle to power the smart switch.

How I would hook it up.

First I would get some red electrical tape and mark the wire to the lamp with red tape.

A switch-outlet hooks up exactly like a smart switch, but without the convenient pigtails. So I would make pigtails.

Get about 7" of 12/3 cable. 14/3 will work if you are sure all the wires in the box are #14. Tear off the sheath to salvage the wires. Then:

  • bare wire to the green screw
  • white wire to the silver screw
  • red wire to the brass screw right next to the silver screw
  • black wire to one of the black screws on the other side

Then I'd join all the wires color to color, remembering you marked the lamp black wire red. Normally you can't count on wire color codes, but I made it work here.

There are more efficient ways to do this, but they are not as clear.

3
  • How would you approach replacing it with this switch: homedepot.com/p/… Jan 27, 2019 at 19:41
  • Would 14/2 cable work? Jan 29, 2019 at 0:57
  • 1
    /2 Doesn't have a red in it, but you can just use more of it and mark a black red. Also if you use 14/ make sure your breaker is 15A. Jan 29, 2019 at 2:24