I want to add a 100 amp RV service panel to my existing, detached garage, 3 wire subpanel. I understand that my current setup is grandfathered in and code is now 4 wire but I won't be able to add this very easily to the main panel. I also understand the risk of a 3 wire subpanel and that an open neutral will put 120V to grounded metal surfaces. I've read through this site and other sites and believe my diagram shows how this would have been wired prior to the 2008 wiring codes. Still, I'd still like the experts to add their inputs. So my questions are, is this the safest way to approach this without adding a 4th wire, and do I need a separate grounding rod at the new subpanel when I already have a grounding rod at the garage subpanel which is about 30 feet away? PS, Part of this diagram was taken from this site, but I wanted to add my own setup to make sure there weren't any additional issues. Thanks and your inputs are greatly appreciated.enter image description here

  • 3
    Personally I would follow code as the safest. Also if an inspector comes out you will have to have followed code for anything you touched. The codes exist for a reason so to knowingly go past one of them is putting yourself at risk – Eric F Jan 22 at 19:39
1

Absolutely not. You cannot run 3-wire to your sub-sub-panel.

You will need to run 4-wire from the grandfathered subpanel to the new sub-sub-panel. You will need land the neutral and ground feeders on neutral and ground buses in the existing subpanel. You will need to separate ground and neutral buses on the new panel.

Tell you a story. A company did a remodel on an old 2-story building. They needed wheelchair accommodations in upstairs hallways and bathrooms. "Why?" they said, "will wheelchair users drag their wheelchairs up the stairs?" (in fact, they do). Three years later, they built another building right next to it, with a 2nd floor walk-between.

The other shoe will eventually drop, you will want to upsize the existing feeder. At that point you will go 4-wire, and since the new extension is 4-wire, you are Code complete.

Save money other ways

The current subpanel has the same breaker size as the intended feed to the sub-subpanel. As such, the $40 subpanel breaker feeding the sub-sub is redundant. Get rid of it. If the subpanel has feed-thru lugs, you can just tap them. Otherwise you can get a lug "breaker" that fits in two breaker spaces but is just lugs.

The sub-sub does not need a main breaker.

AA-8000 Aluminum wire is your friend in feeders (not least, the lugs you'll be attaching to are aluminum, why create a dissimilar metals issue when you're paid not to). You should use 1-1-1-3 Al instead of 3-3-3-5 Cu, so your cable cost will be $100 instead of $250.

3-wire aluminum cable in these sizes is likely AA-1350 alloy, which was outlawed except for service drops/laterals which are outdoors.

I already bought the cable. --->> At these large sizes, most of the cable's value is mineral value. Strip the insulation off and take it to the metal recycler.

  • You make a good point Harper. I do appreciate the input. Maybe best to just spend the time to bring it up to code. – Jay Novak Jan 23 at 14:34
  • @JayNovak in that case I should have elaborated. Grounds can be retrofit, so it is possible to run just a ground wire (on a different route, even) without tearing up the 3-wire cable. – Harper Jan 23 at 16:52
  • Thanks Harper. I was thinking about going that route anyways. I thought I could pull out what was already there between the garage and the house with a snake and the wire that is already in place looks to already be 1-1-1 Aluminum and then just pull it all back with the ground wire attached. My box in the garage doesn't have a separate ground/Neutral bar but at this point for $50 I might as well upgrade that too. I guess I just didn't want to tackle trying to fish that ground wire from the house to the garage. At least this way I can do what I want without worry. – Jay Novak Jan 23 at 18:31
  • @JayNovak Hold on. It's conduit? If it's metal conduit all the way (and not just a cable guard at the start/end), metal conduit itself is a legal grounding path if contiguous. And not rusted out. – Harper Jan 23 at 18:36
  • No it isn't. The house and garage are connected through a big underground PVC pipe. No lines or metal pipe between the two. – Jay Novak Jan 23 at 21:02