I've collected all of the facts about my system and the problem we are seeing. We have two external air pump units outside the house and a Rheem furnace (GH36S, 36000 BTU) that appears to be working. One side of the house gets heated, the other doesn't. I'm hoping the details provided will help give some idea of the problem and some concrete steps that I could try next. I can also grab a voltmeter if needed.
Furnace
furnace-image
Motor Housing
I cleaned a lot of dirt off of the fan behind the motor housing.
motor
Furnace Board
Cleaned and reseated the connectors on the furnace control board. BTW - The controller light is steady green and stays on when I use the front thermostat at high temperature but goes off if I set high temperature for the back of the house and leave the front thermostat at a lower temp.
furnace-mother-board
Thermostats
There are two Honeywell thermostats controls when turned higher than the current room temperature will start the blowers (the one in the front can and does heat the house). With the thermostat in the back, the fan starts and within a min stops again (doesn't stay on long enough to get hot).
Honeywell #1 hw-01-back
Honeywell #1 (Wall) hw-01-wall
Honeywell #1 Faceplate hw-01-face
On the other side of the house, within a minute or two of changing the temperature, the fan sound will stop and the house will not heat up.
Honeywell #2 hw-02-back
Honeywell #2 (Wall) hw-02-wall
Honeywell #2 Faceplate hw-02-face
External Air Pumps
I've never actually seen these things spin up. The furnace is blowing a lot of air though.
Air Pump #1
Serves the front of the house. We have heat in that area (according to the thermostat). I also feel some air blowing, though not too hot but as noted the thermostat is rising.
ap-front
Air Pump #2
Serves the back of the house and if I turn the front thermostat off or to a low room temp, the air does not blow consistently. It starts up for maybe a min or so then turns off. When I keep the front thermostat on, air blows through the front of the house but not the vents in the back.
ap-back
Clicking Sound
A clicking sound appears to be near air pump #2 in the back of the house. I thought it might be from the unit itself so I opened the panel to see if we might have a failed capacitor. An additional (related) complaint is that in the winter the air conditioner is not blowing in the rear of the house.
Expected a Capacitor
On opening, the power panel of the air pump #2 shows some kind of transformer. I do see what is probably a capacitor for the unit inside the unit itself ~ if I look between the vent openings of the top (it's cylindrical and connected to wires from the relay).
hardwired-airpump-2
Breaker Panel
I've checked the roof and garage for additional furnace as requested and I can confirm that we only have a single furnace. As requested please see the house panel.
breaker-panel
Next Steps
I am considering popping off the top of the air pump #2 unit and seeing if I can get the part number for what appears to be the capacitor. Before I go that far, I'd be thankful to hear from the community about what these clues could indicate as the problem.
Would the capacitor be the large cylinder on the inside of the pumping unit? If so, can I assume that it's replaceable like all other capacitors? Please let me know if I may be missing anything or if the clicking sound might indicate a different issue. I am kind of focused on the problem being either at the pump or the thermostat.
  • Just to confirm: You have two outside units, two thermostats, but only one indoor furnace/air handler? Commented Dec 31, 2018 at 1:09
  • Each of the outside units has pipes running into an inside unit. I suppose it could be both into one unit - not sure if that is an option or not - I am not an HVAC tech. But my general understanding is every outside unit is paired with an air handler inside. Take a look at your breaker panels and see what is listed relating to HVAC - could be listed as Furnace, Heat Pump, HVAC, A/C, etc. Even better, post pictures of your breaker panel(s). Commented Dec 31, 2018 at 5:00
    What's going on with the A/C breakers in your panel? They're both double-stuff (quadplex) breakers, and I suspect the 50A half feeds the outdoor unit, but what does the other half (20A or 30A) power? Commented Dec 31, 2018 at 20:33