This is new construction...concerned about voltage drop. The house is a ranch style.I am installing a breaker panel in my garage. I am currently running the wiring (12-2) on a 20 amp breaker for the outlets in my bedroom. Since I have quite a few doors I am going up and down the studs adding quite a bit of length to the furthest circuit. Furthest length approx. 160' . According to a voltage drop calculator 12 gauge should be run. The question I have is: Can I run 10-2 wire to the 1st receptacle in the room and then continue on with the remaining receptacles using 12-2 ? (I would end up with about 80' of 10 gauge to get to the bedroom and then the remainder 12 gauge.)

  • Do your local codes give any specifications as to minimum gauges for that length? – IronEagle Dec 20 '18 at 1:45
  • How about installing a subpanel closer to your actual loads? Cheaper than all those #10 homeruns. – Harper Dec 20 '18 at 1:45
  • Have you considered routing the homeruns in a fashion that doesn't add so much length? – ThreePhaseEel Dec 20 '18 at 2:01
  • Will check with county on this soon. Yes Subpanel move is possible. The one bedroom is the issue so I would only need one homerun. The other rooms are not a problem. – Jim Dec 20 '18 at 2:27
  • 3
    Possible duplicate of Can different gauge wiring be used in the same circuit? – Daniel Griscom Dec 20 '18 at 13:42
0

The answer is yes, you can mitigate voltage drop by running a larger wire to the first outlet, then normal size wire from there. Voltage drop is additive.

Let's say you run 10 gauge 100' to the first outlet and 12 gauge 60 feet to the last outlet, and you have the full load of 20 amps on a duplex receptacle at that last outlet. (Very unlikely but just as an example.)

You'd drop 4 volts on the #10 to the first outlet, then another 3.8 volts on the #12 to the last outlet, for 112.2V - that would be marginal, 6.5% voltage drop. (Just used an online calculator for these calcs, but they seem about right.)

I am getting #6 wire to keep 120V at full load of 20 amps under the NEC recommended 3% voltage drop. Nobody would do that but that's the actual worst case. In reality it's pretty rare to see voltage drop problems with #12 wire in residential systems.

Is it important to keep the voltage drop to 3%? Would 5% be OK? What's the limit? Depends on what the utility delivers, it may be under or over 120V. Lots of things run fine on a wide range of voltage, others are very fussy about voltage.

Will the load really be 20 amps? Maybe every morning with a space heater and a hair dryer running, more likely well under that. Could you get by with a 15A circuit? What will the actual load be?

Can you route the cables differently to shorten the run? Could you run it more staight line to the first outlet through the basement or attic, or maybe just bore holes higher in the walls to miss the doors?

If you really want to keep voltage drop really tight, your might have to consider rearranging things with a subpanel at the other end of the house. That will take some effort and expense, and you'll have to find a spot for the subpanel, but you may offset that with savings on wire and long convoluted pulls, and it will free up some space in your main panel.