If I turn my fan on on my thermostats the heat pump turns on with heat or cool setting
There is a jumper wired from green to w1(the heat pump)
If I move the jumper to r (24v) and g and turn on the dip swith 8 (on - fan comes on with call for heat off - fan comes on with cool call) will it fix my problem?
I’m assuming I would have to adjust the dip switch for summer or winter?
We recently got a wood stove in step down den and it has a blower so we want to run the fan to circulate the heat from it
  • What make and model is your air-handler/indoor-unit/furnace? – ThreePhaseEel Nov 26 '18 at 2:23
  • TZ-3 totalzone trolatemp I have a heat pump and a thermostat on my 1st and second floors all electric units air conditioning and heating back up is comfort – Andrea Jialanella Nov 26 '18 at 2:26
  • No, that's your zone board -- I'm asking about the actual air handler that has the indoor coils for the heat pump in it. – ThreePhaseEel Nov 26 '18 at 2:28
  • Comfortmaker model fxm4x3600A – Andrea Jialanella Nov 26 '18 at 2:29
Remove the jumper to G, turn dip switch 8 on, and enjoy.
The jumper between W1/Y1 and G on your board is what is causing the fan problem here. So, I would remove the jumper to the G wire (from W1/Y1) from the zone board with the indoor unit OFF at the service switch, flip dip switch 8 on the zone board to ON to make it so that the zone board calls for fan when a heat call comes in, turn the service switch on the indoor unit back ON, and enjoy your newfound comfort!
  • Should I switch dip switch to off during cooling season? If so do I need to turn the main off to slip a dip switch – Andrea Jialanella Nov 27 '18 at 14:54
  • @AndreaJialanella -- you do not need to change the DIP switch between heating and cooling seasons. – ThreePhaseEel Nov 27 '18 at 23:10
  • Y1 is jumpered from w1 and w1 is jumpered to g(remover and fan works) should I also remove the y1 to w1 jumper ? If so nothing will be running to w1. Should a jumper run from w1 to w2? – Andrea Jialanella Dec 1 '18 at 16:13