I'm in the process of upgrading a bunch of switches in my house to TP Link Kasa smart switches. I just opened a switch box and I don't understand the wire configuration in it, and was hoping to get some explanation about what's going on.

Here's what I see: enter image description here

When I turned off the breaker switch that I thought was controlling the power to this switch, the switch did stop working as expected. But when I tested the terminals on my switch with a multimeter on AC voltage setting, I was surprised to see that the display showed me ~120V. I turned off the breaker switch for the adjacent room and redid the test, and this time the display showed me ~0V.

To test this further, I separated the three black cables to test them individually, and the results are as follows:

Black 1: 0.025V
Black 2: 1.608V
Black 3: 118.2V

Another interesting observation, after separating the black cables, the light switch in the adjacent room stopped working.

Any explanation about what's going on here would be much appreciated!

  • 0.025V and 1.608V are phantom voltages - induced from other wires - don't worry about that. What you should have typically is one cable from the panel, one cable to the light and one cable going on to elsewhere. That is how it looks like things are wired, but that doesn't match the breaker issues. With the blacks separated, see what voltage you get with breaker 1 & breaker 2 each on and off (with both off should be < 2V everywhere) - i.e., all 4 possibilities 1 on/2 on, 1 on/2 off, 1 off/2 on, 1 off/2 off. Then we can get to the next step. – manassehkatz Nov 25 '18 at 23:01
  • Does your breakers interrupt only hot or both hot and neutral (this is typycal for RCDs) ? – DDS Nov 25 '18 at 23:14
  • 1
    Can you put a test light from Black 3 to Neutral with the breaker for this circuit off and see if it lights up? – ThreePhaseEel Nov 26 '18 at 1:55
1

Just looking at the connections in the switch box and the voltage readings on the separated wires, it appears that cable 3 (lower right) recieves power from the service panel, cable 2 (lower left) supplies power to adjacent rooms, and cable 1 (upper left) runs to the light fixture. - What is completely surprising is the actions of the two circuit breakers.

Perhaps you should begin by reconnecting everything. Then, switch off the circuit breakers individually and in combination, and note which switches and lights stop working in each case. If you find anything that goes dark when either breaker is off, or anything that goes dark only when both breakers are off, then your house is dangerously miswired and you need to fix it before installing anything new.

1

When you add a light, you don't have to bring its power supply cable all the way back from the main panel. You can simply extend from somewhere else in the system that already has always-hot and neutral.

That is exactly what cable 2 is doing.

Cable 3 brings supply from the panel (or another outlet). You know what cable 1 does.

By "cable" I mean the gray things with multiple wires in them.

0

Black 3 is the phase coming in (permanent line coming in), black 2 is is a phase 'looping through' (also permanent line but going out): it feeds the switch in the near room. Black 1 (switched line) is the switched loop controlling your light fixture (in newer installations it's a red wire).

White are neutrals pigtailed together because neutral should not be interrupted

  • 1
    You have described the normal implementation. But the breaker actions don't match. – manassehkatz Nov 25 '18 at 23:05