1

I'm installing a panel with the feed conductors entering via 1-1/2" PVC. Is an end bushing, as shown here (for example), required by the U.S. NEC for PVC?

enter image description here

image source

3

From the NEC:

352.46 Bushings. Where a conduit enters a box, fitting, or other enclosure, a bushing or adapter shall be provided to protect the wire from abrasion unless the box, fitting, or enclosure design provides equivalent protection.

The important part is bolded above - you need a bushing unless your fitting provides equivalent protection - that is, equivalent to the protection a bushing provides.

You'll probably terminate your conduit in your panel with either a PVC male terminal adapter:

male terminal adapter

or a PVC box adapter:

box adapter

I think anyone would agree the box adapter provides protection equivalent to a bushing.

I believe it's generally accepted that a PVC male adapter does provide equivalent protection, but you might find someone that disagrees, and some of them are pretty sharp. I usually ream them with lineman's pliers to take the edge off and do without the bushing.

The box adapters make a great connection but since they are cemented on, they are a pain if you have to remove and replace them.

| improve this answer | |
1

A bushing is typically NOT required when using PVC conduit. However, for the sake of completeness I always use a bushing...

| improve this answer | |
  • Thanks. Please revise to elaborate on what "completeness" means here. Aesthetics? A personal standard for some purpose? – isherwood Nov 12 '18 at 15:27
  • By completeness I mean I'll do it even if it seems to be or is overkill. This is my personal preference tho. – BillWeckel Nov 12 '18 at 15:37

Your Answer

By clicking “Post Your Answer”, you agree to our terms of service, privacy policy and cookie policy

Not the answer you're looking for? Browse other questions tagged or ask your own question.