0

Suppose you wanted to put a second oven next to the existing oven in your kitchen. Could you simply add a second receptacle to the circuit?

Hypothetically speaking, suppose your stoves were a Kenmore 970-678534, and a C970-502123, and your circuit had a 40AMP breaker and I'm not sure what the gauge the wire is, but it's fat, much fatter than the dryer cable. Hypothetically.

  • 2
    why are you asking a hypothetical question? – jsotola Nov 12 '18 at 3:15
  • 1
    @jsotola My best guess is "I already did this and now I have second thoughts and am worried that maybe it was a really bad thing to do but I don't want to admit it." – manassehkatz-Moving 2 Codidact Nov 12 '18 at 3:28
  • Can you post the nameplate wattages of both appliances? – ThreePhaseEel Nov 12 '18 at 4:06
  • Also, are these built-in ovens, slide-in ranges, or free-standing appliances? – ThreePhaseEel Nov 12 '18 at 4:07
  • @ThreePhaseEel 10.6 & 13 kw @ 120/240 volts, 60 hz, free standing. – ShemSeger Nov 12 '18 at 15:08
1

Nope

NEC 210.23(C) limits 40A and 50A multioutlet branch circuits in dwelling units to powering fastened in place (i.e. built-in) cooking appliances, not freestanding ones. (A regular range circuit only has a single outlet, so it is governed by NEC 210.22 instead.)

Your 40A branch circuit could power either range, though, as a 13kW nameplate range comes out as 8.4kW of demand-factored load when you apply Table 220.55, note 1 to it, and NEC 422.10(A), paragraph 4 expressly permits the table 220.55 branch factors to be applied to household cooking appliance circuits.

  • Do you happen to know how similar the NEC and CSA are? I live in Canada. – ShemSeger Nov 13 '18 at 16:41
0

Hypothetically, no. Realistically, also no. Legally, still no.

  • 1
    I wouldn't go that far, not without 220.55 numbers in hand at least. – ThreePhaseEel Nov 12 '18 at 4:06
  • I know I've seen some other answers recently regarding 2 dryer receptacles on one circuit. I'm not so sure it is prohibited. Hypothetically :-) – manassehkatz-Moving 2 Codidact Nov 12 '18 at 4:13
  • 1
    @manassehkatz because the Code for 30A circuits says nothing to prohibit multiple receptacles, and other code is permissive. The Code for 40A and 50A receptacles explicitly outlaws multiple receptacles. I believe it's NEC 240.4? – Harper - Reinstate Monica Nov 12 '18 at 21:54
  • @Harper -- 210.23(C) is the governing Code here, as mentioned in my answer – ThreePhaseEel Nov 13 '18 at 1:17
0

Based on your watt numbers, the breaker couldn't power one of those, let alone two.

A 40A breaker is good for 9.6KW at redline.

That won't cover even the smaller 10.6kw load, let alone the 13kw load.

I would say the one should be installed with a 50A breaker (12kw) and #6 wire, unless the instructions say to do something else, in which case follow the instructions. The other one should use a 60A breaker (14.4kw) also with #6 wire. Each one will max out its circuit.

You are not allowed to put two receptacles on a 40-50A circuit, nor can you put those receptacles on any other size of circuit. Each will need its own circuit.

  • Actually, a 13kW range fits onto a 40A circuit as it's only 8.4kW of demand-factored load once you apply Table 220.55, note 1 procedures and the last paragraph of 422.10(A). – ThreePhaseEel Nov 13 '18 at 1:16