I have an electric furnace that has power, fan, electric heat, but I do not have a "C" wire. The thermostat wiring has several unused wires that are routed to furnace. It is a matter of applying 24VAC to the existing Blue wire that would be "C" wire. Why can't I jumper the 24VAC Power (red) to the C wire? I know there is a 24VAC transformer, but not sure if I should mess with it.

bumped to the homepage by Community 2 days ago

This question has answers that may be good or bad; the system has marked it active so that they can be reviewed.

0

You have things the wrong way around

The way conventional mechanical thermostats work is similar to a wall switch -- you only need to provide constant 24VAC power (R) and a switched-hot to the load (W/Y/G) in order for it to be happy. However, modern electronic thermostats either recommend or require a return path for their own internal power -- the C wire you are talking about is that return path to the other side of the 24VAC transformer, same as how a neutral in a mains circuit returns electricity back to the utility's service. So, it needs to be connected to the C terminal on the control board, or to the same point the C wire from the air conditioner outdoor unit/compressor connects to (find the wire from the air conditioner that connects to the Y wire from the thermostat -- the other wire in that cable connects to C, considering that you have a conventional air conditioner).

(If you tried jumpering the 24VAC power (R) to the C and R terminals on your thermostat, it simply would refuse to turn on as there would be 0V across its internal power circuitry, provided another power source such as batteries or a power-stealing circuit is not present of course.)

Your Answer

By clicking “Post Your Answer”, you agree to our terms of service, privacy policy and cookie policy

Not the answer you're looking for? Browse other questions tagged or ask your own question.