I purchased a new water softener for the house. It has a digital flow metering device. It worked great for a few days and then stopped working. Long story short, I finally figured out that the outlet I plugged it into was for 240V instead of 120V (bought the house about a year ago so the previous owner obviously didn’t know what he was doing). The power supply for the water softener has a 120V to 24v stepdown transformer to power the digital meter. I’m assuming the water softener was getting 48V for a few days until either the transformer or digital meter gave out. I’ve corrected the electrical problem so now it’s time to get the water softener working again. Will replacing the transformer be enough or should I just order a new digital meter? $30 vs $300 so I’m hoping for the best case scenario.

migrated from electronics.stackexchange.com Nov 5 '18 at 17:13

This question came from our site for electronics and electrical engineering professionals, students, and enthusiasts.

  • Try reconnecting your flow meter to the 120V, there is a chance that it may work. I cannot see that you have anything to lose. Some devices have fuses that reset after cooling. – Steve G Nov 5 '18 at 15:32
  • I’m waiting for a new transformer. I’m pretty sure the original and a replacement that I had ordered are ruined since I get 0V when plugged in. Unfortunately, I didn’t realize the problem until after I ruined the 2nd transformer. – L Moore Nov 5 '18 at 16:10
  • 24V transformers are super common and should be found at any HVAC suppply for under $25 or Amazon for $13. They are universally used in furnace controls, and come in several mounting styles including "in a knockout" or "as a junction box cover". – Harper Nov 5 '18 at 17:57
  • Some digital controls have Pico fuses they look like a resistor and don't smell when they blow, with the model number we may be able to find a schematic and find a 5$ or less part that can be replaced. Some Pico fuses are soldered but some have sleeves that the fuse leads slip into look closely at the board it may be that simple. – Ed Beal Nov 5 '18 at 18:55
2

It's impossible to say. It really depends on how the meter's internal power supply works.

Being electronic, obviously it runs on DC and not 24VAC. They're just using that voltage because it's extremely common in North American homes, being used as control voltage for the furnace and there's usually an existing 24V transformer somewhere in the house. Those transformers are cheap and common, by the way; I'm surprised you have to wait for one. Any HVAC supply will have them, maybe even a hardware store or big-box.

So it must have an internal power supply. If it's a switching power supplY, they open and close (switch) a gate, and on higher voltage they simply close the gate sooner. (That is how many consumer electronics can auto-range from 90-264VAC). So you can run switching supplies beyond max spec if their insulation is in good enough shape to handle the higher voltage. Insulation is cheap to add to most components (not electrolytic capacitors), so you have a fair chance. If it's fried and you want to attempt component repair, start with the big caps.

None of this will fix anything else that was plugged into that 240V receptacle.


Putting 240V on a NEMA 5 120V receptacle is simply outrageous. And needless - they make receptacles for that. They look exactly like standard receptacles except they are keyed differently. Every big box store and hardware store sells the receptacles and plugs.

enter image description here

Now if you found a NEMA 6 receptacle and altered your transformer to fit, that's on you. But if the previous homeowner fit a NEMA 5 receptacle because he was too lazy and cheap to get the correct NEMA 6 at the hardware store, and his logic was "well I know it's wired 240V", then he should have disclosed that in his disclosures, and he would've been written up for it and had to fix it, presumably by installing a NEMA 6. If he did not do any of that, then he is liable for all your damages here. I would go after him for it. Not least, he sorely needs an education, because you bet he did it again to save $5.

This could have caused a house fire.

1

Really sorry that you were exposed to an improperly wired outlet and had to discovered it this way. If you have already not done so you should take a meter and measure the other outlets in your house that the previous owner may have messed around with.

You could measure the transformer output when it is plugged into the proper 120VAC outlet. If it reads out ~24VAC then the transformer is probably OK. I would expect that the maximum voltage ratings of the transformer were above those that it was exposed to in the improper operating scenario. So it should be OK unless you noticed that it got extremely hot for those few days in which case I would recommend replacing it.

The digital metering unit on the other hand has likely not had a good outcome from being exposed to the 48V for an extended period of time. It is not possible to know, without reviewing a schematic for the metering unit, if the unit was designed to work properly with a wide range of input voltage or not. Certain designs could have exposed much of the circuitry to voltages well beyond what it can survive. On the other hand there could have just been a small portion of the circuitry that was exposed and failed but left the rest OK. In this latter case an experienced electronics technician could possibly repair the unit by replacing just a few components. You would have to weigh possible repair costs against the cost of a new unit.

  • Yes I’m planning on checking all outlets this week. Thank you for the advice. I get 0V when testing the transformers so I’m waiting for a 3rd replacement to arrive to see if the digital metering unit survived. Sounds like I may be better off replacing instead of repairing the unit. That’s what I was afraid of but needed to know. Thank you for your response. – L Moore Nov 5 '18 at 16:14
0

The transformer will, to some extent, limit the voltage at the output, likely to more like 36V than 48V due to saturation. Your meter may or may not have survived intact. If nothing appears to be burned (use your nose) it may well be okay.

Most well-designed products will have no trouble with a momentary transient but they may not be able to withstand continuous abuse.

  • Everything looks good and no burnt smells. Since the water softener is not inside our home, I’m not sure exactly how long it worked for on the extra voltage it received. It took me 2 weeks to realize it wasn’t working. That’s when I checked on it and realized it wasn’t on. – L Moore Nov 5 '18 at 16:38
0

I suggest you to get a 'switching' power supply capable of bearing 110 to 250V (similar to pc power supply) so you just don't have to bother where you connect it. 'Standard' power supply, that are essentially transformers, only get 'proportional' reduction ratio (so a 220V to 24V used on 110V circuit will make 12V and vice versa). Anyway, in your case, it's possible you have destroyed your softener (instead of your transformer).

  • This might work if DC but many of the low voltage devices use AC in parts of the controll circuits like 24v AC motor to actuate the valves but we know the digital board uses DC this is true, we would need to know the model number to figure it out. – Ed Beal Nov 5 '18 at 18:50