2

I recently purchased the ecobee3 lite and am now stuck trying to install them. I have 3 Honeywell thermostats I am looking to replace and my heating system is oil/hot water. My home was built in 1970 and I believe the wiring involved here is pretty old. I am not an electrician but I believe I should be able to handle this project given some help.

For starters, each of my thermostats is hooked up with a red and a white wire, with one additional (blue) wire coming out of the jacket in the wall, but not hooked up to the thermostat:

thermostat wiring

As far as I can tell, there's no voltage coming from that wire. I checked with a multimeter and it came up 0 every which way I checked it. So then I made my way to the furnace. Here's what I see:

furnace wiring

So this box is a Honeywell Aquastat Relay L8148A whose schematic can be found here.

Here are two angled views of the controller that give a better picture of the few different connection points:

left side of the controller right side of the controller

Here is the inside of the cover plate for the controller that details the wiring a bit:

inside the cover

As you can see, the main controller has 1 pair of red/white wires labeled Thermostat in the top-left corner. Then there are two transformers affixed to the furnace that also have red/white wires. I'm at a loss because most "add a c-wire" videos show a controller that has 5 different connection points, one of which is clearly labeled C, and they run a wire from there and everything works. I can't find a spot that I'm confident would be a "C" wire spot. The ecobee3 lite offers a PEK but that looks like it also requires more than just two wires to be run into it to operate properly. Many of these smart thermostats assume you are also controlling a cooling system which I am not; I only have a furnace.

So my question is: Can I install an ecobee3 lite myself in this system without a ton of work, or should I just buy something like the Nest E that can power-steal from my furnace?

7
  • 1
    You seem to have enough transformers there that you could power an ecobee, and might be able to even do it purely from the aquastat relay box if you find the right connections. You might need to run a new cable, though, because this one appears to only have two conductors (at least at the end connected to this relay). See also: support.ecobee.com/hc/en-us/articles/… Oct 2, 2018 at 21:07
  • So are you saying that if I found where that third blue wire was going in the basement (presumably nowhere) I can run it to one of the transformers on the boiler and connect it at the same point the white wire is connected? Oct 3, 2018 at 12:10
  • Yes, you will need to find that blue wire.
    – longneck
    Oct 3, 2018 at 15:24
  • See my answer to a similar question.
    – Tester101
    Oct 15, 2018 at 16:16
  • While Shimon Rura's solution may have worked for you, it's not the proper way to do this. The thermostat is being powered from the transformer in the aquastat. Grabbing a C wire from a completely separate transformer is not proper wiring.
    – Tester101
    Oct 15, 2018 at 16:24

3 Answers 3

1

You have a bigger problem than chasing down a blue wire here

Here's the rub -- the Honeywell L8148A doesn't even provide a C terminal for the blue wire, PEK, or whatever to connect to, as it was designed for dumb mechanical 'stats. Considering it not only contains a transformer and relay, but a high limit function as well, this leaves you with limited options -- simply replacing it with a separate transformer and relay won't do. One could add another transformer and relay as an isolation relay, but that's probably more complexity than is called for here, considering that Honeywell makes a more versatile version of what you're looking at, called an L8148J.

Replacing your L8148A with an L8148J configured for a 24VAC gas valve (valve from B1 to B3) lets you connect the C wire to the TV terminal, jumper T to TV, and then pull the jumper from Z to W, connecting R to Z and W to W. Of course, this all presumes that the cable doesn't transition from 3-wire to 2-wire somewhere in the middle; if it does, then you need to use a PEK or add-a-wire device to handle the situation atop the aforementioned aquastat changeout.

0

If you can't find the blue wire, then the next best thing the Ecobee's Power Extender Kit. Every Ecobee thermostat comes with one.

Ecobee provides excellent installation support. If you can't use their included instructions to install the Power Extender Kit, then you should call them.

-1

You will want to wire your thermostat with three wires, called R, W, and C. Red is "supply voltage", White is "calling for heat", and Common (often blue) is a ground wire, allowing the thermostat to receive power even when the R-W circuit is switched off. Old-style thermostats are, electrically, simply a switch that connects R & W, which are connected to terminals on your aquastat. So R&W are interchangeable, which is why they're both labeled T/T.

For your new thermostat, it expects to have 24VAC potential between R & C. When calling for heat, it will connect R & W. So you need to identify (using schematics and/or a voltmeter) which of the two T/T terminals you should connect to R, which to W, and where on your aquastat you can connect C. If your board doesn't have a convenient terminal for C, you may need to splice into one of the output legs of the 24VAC transformer.

Once you have a theory of how to do that, it's easiest to try it in the basement standing next to your boiler/aquastat relay. Shut off power to the aquastat relay, wire up the ecobee sitting there in the basement, and then turn on the aquastat. If the ecobee boots up properly, try turning the heat on and confirming it activates the aquastat (you should hear the aquastat relay click, and a circulation pump should turn on). Now you know how things should be wired, and you need to figure out how to connect the cable.

For the cabling, you can either:

  • run a cable with 3 or more wires run between your thermostat and the aquastat relay - the same as your test rig, but longer; or
  • maybe use a common maker or isolation relay, depending on the availability of space, power, and the common maker's requirements (for your case I think you're right that the ecobee PEK won't work, but something like the Fast-Stat Common Maker might).

My first step would probably be to check the cable - if it's relatively easy to pull some new thermostat cable through, that's probably your best option. If you can't get a 3-wire bundle between the aquastat relay and this thermostat, then consider things like the common-maker or a power-stealing thermostat.

1
  • Uh -- there is no C terminal on an L8148A aquastat... Oct 4, 2018 at 1:44