I did some wiring and want to make sure i calculated it all safely. I have a 30 amp breaker, single phase 240volts wired to a dryer outlet, don't know the awg of that as it's in the walls and has been built a while ago. I then attached a extension cord to the dryer outlet that is 50 feet long made out of 10/2 solid wire inside a armored conduit. I am drawing a constant 23 amps and the wire feels pretty warm. I can hold it it's not like super hot but it feels pretty warm. Now considering the legenth of wire and the amps being drawn I should be good and the calculations online say I should use 12 awg but I had 10 lying around. Also is solid core better in this case than stranded/braided (whatever its called)? I also will be drawing a constant 23 amps for 10-13 hours but then nothing for about 12 hours after that. So am I safe here or do I need to make my extension cord with #8? Or with stranded wire? I just figured that solid core will safely transmit power better and safer than the other stuff that's why houses use solid wire in the walls. Thanks for the help.enter image description hereenter image description here
13
  • When you say 'wire inside a(sic) armored conduit" are you talking about type AC cable, type MC cable, or wires or a cable stuffed down a flexible metal conduit (FMC/"greenfield")? Sep 24, 2018 at 2:22
  • I'm talking about this wire just lying on the ground being used as an extension cord m.lowes.com/pd/250-ft-10-2-Solid-Aluminum-MC-Cable/3637694
    – rasmukri
    Sep 24, 2018 at 2:34
  • How many prongs does this dryer outlet have, and what voltage(s) does the thing you're powering require? Sep 24, 2018 at 2:43
  • 3 prong outlet and I'm drawing 240 volts. 2 hot and 1 ground, no neutral
    – rasmukri
    Sep 24, 2018 at 2:50
    If ground is physically cabled to this location, change it to a NEMA 14 receptacle and don't look back. This is pure upgrade, and the landlord would be insane to object. If there is a dryer which also must plug in there, just also change its cord to NEMA 14, there is a simple procedure for doing that. This is 100% pure upgrade in all respects, no downside for anyone. Sep 24, 2018 at 6:22
Your wire sizing was perfect
First let me say you did an impeccable job sizing the wire.
You have a 23-amp load. It might commonly run more than 3 hours at a time, so Code designates it as a continuous load. On most circuits, continuous loads must be derated by 125% -- that means when you provision power to them, you must provide electrical service as if they are a 28.75A load (23A x 125%). Good for 30A with room to spare!
Boy, it's almost like they planned it.
In fact, they did. 23A is a very popular appliance size, and applies to almost every dryer and most water heaters.
So yes, you sized the wire just right.
Whatever calculators online said you shoulda used 12AWG are wrong. It's easy to misinterpret things, such as what's allowed in electronic inside-chassis wiring, or the 90C column of the ampacity charts. (12AWG is 25A@75C, but then, the wire would be 75C all the time.)
A few details, though...
Solid wire and stranded wire have exactly the same ampacity.
I'm not sure exactly what you mean by "extension cord" but I'll take it at face value. Cord must be cordage, such as SJOOW - which has tough insulation and highly stranded wires designed to be flexed, draped, move a lot, be stepped on, and all the routine insults that cordage must endure. Using in-wall wire such as NM, UF, AC or MC as a "substitute for cordage" is not particularly safe. Repeated flexing damages solid wire, leading to overheating and series arcing.
But then, I don't know what your use is. You're not supposed to use flexible cords as a substitute for the permanent wiring of a building, but the wire you have is made to be permanent wiring in a building.
That socket is also a huge problem. It's a very old NEMA 10-30 design which predates grounding in houses. It brings hot-hot-neutral (because some apparatus inside dryers is 120V). For ground, it was never intended to be grounded. NFPA wanted to require grounded dryer sockets (NEMA 14-30) about the same time they started requiring grounding generally. However, the appliance lobby had a conniption: they didn't want to lose sales over socket confusion, so they begged NFPA to allow NEMA 10 "since dryer plugs are rarely ever disturbed, the chance of a wire failire is low" and therefore "just attach the dryer chassis to neutral" Say what???
This is exactly the load of malarkey it sounds like: bootlegging ground off neutral. Illegal and stupid everywhere else. And in your case, that old socket is getting a workout, so neutral could fail. Those large sockets are not made for frequent change.
Usually people are stuck at NEMA 10 because the cable from the panel is 3-wire and hard to replace. However in your case you have the 4-wire cable from the panel, so most likely someone downgraded the socket from NEMA 14 to NEMA 10 because they did not realize how easy it is to change the dryer's cord to NEMA 14. The NEMA 14 socket has the same formfactor as the one in your photo, and a change would not even be noticeable.
Anyway since you require ground (and not neutral) you might as well change it over to the universal donor, NEMA 14. You could make do with a NEMA 6 (hot-hot-ground) but dryers can't use that.
Code has large safety margins built in. At 23 amps 125% is still under the 30 amp rating so the wire will be fine for current carrying capacity. Other than the outlet type mentioned in the comments I would have a concern with solid wire used as an extension cord (if flexibility is needed) solid wire will fail much sooner than stranded so if the cord is being moved around or subject to vibration change to stranded. Your load of 23 amps x 125% = 28.75 and the wire is rated for 30 amps. I thought I would add that I mention the safety factor 10 awg wire in a control cabinet can be protected with a breaker up to 160 amps and 90 amps going outside the cabinet, these are for motor circuits and controls but NEC table 430.72.b can give an idea of the safety margin built into code , as 10 AWG is limited to 30 amps per table 310.15.B.16 and limited by 240.4.D.
  • In addendum - also the NEC requires a all dryer outlets in a residence to be rated at a minimum 5000 VA (watts) which is covering any dryer that may be installed in a residence not just the current one. It also states that any 30A circuit installed in a residence only carry 80 percent of the branch rating. That's why a standard dryer outlet installed during construction has a 30A breaker and a #8 wire is used as the conductor and a NEMA 1430 receptacle is installed. Sep 24, 2018 at 14:45
  • So the house has #10 wire already I'll talk to my landlord about changing it to the 14-30 outlet. I don't need flexibility as the extension cord is not moving once it is in place. I just wanted to make sure it was safe and I'm not going to burn the place down with #10 wire under the constant load thanks
    – rasmukri
    Sep 24, 2018 at 15:50
  • A 5700w 240v dryer would still be legal on a 10 AWG circuit protected at 30 amps, 5700/240= 23.75 x 125%= 29.7 amps
    Sep 24, 2018 at 16:26
  • Landlord said no to changing the plug. Also I am NOT powering a dryer. It is to charge my Tesla which requires hot hot ground, NO neutral. So I added a new pic to the original post is that safe and good to go. I woire capped the neutral and put the ground wire in the ground spot. I already verified it is grounded in the circuit box to the main ground strap.
    – rasmukri
    Sep 24, 2018 at 16:31
  • I understand you are not powering a dryer I was responding to RME's comment.
    Sep 24, 2018 at 17:13