0

I've read the posts regarding no neutral line on a 240v circuit, this was my situation, had a new cooktop installed as a replacement, the electrician connected the black and red line from the cooktop to each of the blacks coming from the panel. He then took the neutral and ground from the cooktop and connected to the ground from the panel. Had never seen this before, was this correct ?

  • The neutral may be necessary for a 120V circuit for controls. That is common on an oven (control panel, clock, etc.) but more unusual on a cooktop. It could easily be that the previous cooktop simply didn't need a neutral but the new one does. If you post the specific model # then we may be able to provide more info. But the basic concept is that if a neutral is truly needed then it should have a separate wire (not using ground) back to the panel (a) due to the way ground/neutral are bonded for safety and (b) because ground is not supposed to carry current except in a fault situation. – manassehkatz Sep 20 '18 at 16:08
  • Can you post clear photos of the inside of the junction box where the cooktop is connected to the house wiring? – ThreePhaseEel Sep 20 '18 at 22:27
2

It sounds like this guy wires 4-wire ovens and ranges all day everyday. When you do that, you run into a lot of obsolete NEMA 10 wired circuits, hot-hot-neutral no earth.

It also sounds like he wired this range, he saw 3-wire supply and "ran home to mama" as it were and his muscles just wired it NEMA 10 out of habit.

Older ovens want 120V only so customers can use common off the shelf incandescent bulbs for the oven light. (Incandescents thrive in heat.) Many of the newest ranges, especially those cross-marketed in Europe or Asia, don't need or want 120V at all. They need a Hot Hot Ground connection, or NEMA 6. (NEMA 14, Hot Hot Neutral Ground, will also do.)

If your wiring is old, then you are mistaken about the third wire. It is not ground. It is neutral, and this is a NEMA 10 wiring arrangement. If the cable is /2 USE type and the third wire is a bunch of strands that wrap around the two hots, that was legal as a neutral prior to 1989. In any other type of cable, use of the bare wire as neutral was always illegal, but widely done because NM is cheaper than USE. You can correct this flaw by reclassifying that illegal neutral as a ground, and moving it to the ground bar. If the cable is USE, you can do that too but you are better off enjoying the grandfathered neutral which you are entitled to, and retrofitting a separate ground, which you are also entitled to do.

If the cable was recently installed for the last range whichwas a fancy Eurostyle job that didn't require neutral, they wired it with /2 cable as NEMA 6. Any modern use of /2 can only be NEMA 6 (Hot Hot Ground). That would be a rather foolish thing to do since it cost only a few dollars more to pull /3 cable instead, allowing modern NEMA 14 (hot hot neutral ground) connections which most modern ranges prefer. In this case you are married to NEMA 6, which most ranges cannot use.

So either

  • the neutral-required range must go,
  • or you must pull new cable,
  • unless your setup is NEMA 10 with USE cable, in which case your electrician probably installed it "correctly" in the obsolete NEMA 10 manner. Legal but dangerous, so for safety you should retrofit ground, and separate neutral and ground at the range.

Wait. Did you say two blacks?

Whoa. All modern cable has differing colors - black and red. Two blacks means either a) very old cable, or fasten your seat belt b) the wire is individual wires in conduit.

The Conduit wiring method allows you to add individual wires. If you need a neutral, just get a long enough white #6 THWN-2 wire, and fish it on down the conduit, you're all set! If indeed it is in conduit, then failing to include the white neutral wire was a perfectly reasonable thing to do, since it's so easy to add later.

1

This might be OK, but it might not. You'll have to do some investigation first.

Find the install manual or the wiring diagram. If the cooktop requires a separate neutral, then this is not correct. It may work because the ground is acting like the neutral in this case, but it would not be correct and can be dangerous.

If the cooktop does not require a separate neutral, then it is common for the neutral and ground to be bonded together in the cooktop. If it was done inside the cooktop and a 3 conductor cable connects the cooktop to the junction box or a 3 prong plug was used, then this is OK.

If a 4 conductor cable or 4 prong plug was used, and the neutral and ground were bonded in the junction box, then this is definitely wrong, and probably dangerous.

I think I covered all of the possible configurations.

0

First of all, no one really likes doing this but it is legal under certain conditions and all of the conditions must be met. I have posted this before in case you want to review it. Its NEC Article 250.140 enter image description here

enter image description here

Good luck

  • thanks all for your comments, can't get a clear picture of the box – Phil LeMarquand Sep 21 '18 at 17:09
0

thanks all for your feedback, can't get a clear picture of the junction box, but a little more background, house was built in 1994, so I would think wiring is pretty current. We replaced a Jen-air downdraft with a kitchenaid downdraft kced600gbl, the electrician took the time to read the directions there are instructions for connecting a 3 wire from the panel to a 4 wire from the cooktop, it calls for connecting the white wire from the panel with the white and ground from the cooktop. since I only had two blacks and a ground from the panel he felt it would be safe since this was a "grandfathered" why of wiring also note, the appliance store (not one of the big box type)only placed the unit in the opening we then made arrangements for a large well know electrical contractor in my area to make the connection