I called a plumber to upgrade my water heater. The current breaker is a 20A. The new water heater requires a 30A. But my wiring is #12.
The plumber said, without much conviction, that it's fine for now, and installed the new water heater.
My current setup is:
20A breaker 240V, #12 wire, new water heater.
As soon as possible, I'll upgrade to:
30A breaker 240V, #10 wire.
What's the worst that can happen in the mean time ?
9
    If everything is installed correctly (except not upsized), you should get nuisance trips when the heater draws more than 20A. What is the model # of the heater? Aug 27, 2018 at 14:37
    Is this a one pole breaker (120V circuit) or a two pole breaker (240V circuit)? Aug 27, 2018 at 22:41
  • Look into ThreePhaseEel's question. I edited my answer to cover it. Aug 27, 2018 at 23:57
  • @ThreePhaseEel It's a two pole breaker (240V circuit) Aug 28, 2018 at 17:04
  • @manassehkatz Sorry I forgot to check, I'll look it up this evening. What do you mean by "not upsized" ? Aug 28, 2018 at 17:06
The standard 240V water heater only has one speed (choice of amp draw): 23A. That is how all such hot water heaters are sized. The reason is they want it as fast as possible while falling within a statutory 24A limit.
Edit: ThreePhaseEel brings up an interesting point. A 30A hot water heater implies that it is 240V, because it's cheaper to bump volts to 240 before amps to 30. However, you didn't tell us the old service was 240V (meaning a 2-pole "double" breaker in the panel). If this is in fact a 120V heater, that changes things. I'll describe this difference inside this box.
First, make sure this is a "plain old resistive heater" and not a hybrid or heat-pump heater. The trick I'm about to describe won't work with a hybrid.
Now I said "resistive" - the heating element is a resistor, which is the simplest electronic device on earth, and it follows simple rules, starting with Ohm's Law: Voltage = Current x Resistance. Resistance is defined by how the heater is built. So what happens if we run it on 120V?
Well, since Resistance is fixed -- if Voltage drops by 50%, so must Current. That means on 120V, this same water heater will draw 11.5 amps, and will be within safety limits of a 15A/120V circuit, and will not trip breakers. However since useful power = voltage x current, and both those are halved, useful power is 1/4.
What does that mean for heater performance? Assuming it's Energy Star, the insulation is tip top. It will reach target temperature ........... eventually. And it will take 4 times longer to get there. You'll want to follow the conservation tips in my last paragraph.
This use on 120V is safe, and it's safe indefinitely.
Now back to the 240V scenario.
All of the advice to follow violates Code. The only Code-correct solution is correct cable and breaker, but you knew that.
So expect a lot of breaker trips.
Wait 1 hour before resetting it. That is because of this particular situation - we know exactly why it is tripping, so the consequences of resetting it too soon are also known.
If you upgrade the cable to #10 copper (10/2 will suffice), then you can reset it as often as you please. I am assuming perhaps it is hard to obtain the right breaker due to obsolescence (PushMatic) or complexity (quadplex).
If you have a Federal Pacific, Zinsco or Challenger panel, those panels are dangerous and you are already playing with fire, so don't push your luck with those panels.
You will have fewer trips if you take great pains to use hot water VERY sparingly - follow California drought or boondocking-in-RV rules. Get wet, shut the water off, lather up, then do a quick rinse... Select cold water in dishwasher and washing machine... Let the soap do the cleaning not the heat... Etc.
    If his HWH was hooked up to a 120V circuit, then his breaker won't trip -- he'll just get a rather lukewarm performance from his HWH. Aug 27, 2018 at 22:42
  • Thank for your explanations. It's a two pole breaker (240V circuit). I already found the perfect 30A breaker. The main issue is rewiring (through walls) from #12 to #10 which I'll leave to a professional in the next few weeks. The part that surprises me is that I thought the breaker would trip when the heater drew massive amount of electrity and I assumed that would happen when first plugging it in, since the water is completely cold... and it didn't trip yet, surpringsly. Aug 28, 2018 at 17:18
    Thank you everyone for the warnings and concerns :) The 30A breaker is sitting on a shelf. I will install it only after I have #10 wires in the walls. Aug 28, 2018 at 17:28
    I'll lower the temperature as a precaution and hurry to fix the problem. Aug 28, 2018 at 17:31
    I would just move the white wire off the breaker and onto the neutral bar, making it the 120V scenario described in the yellow box. You can run that way forever without worry. Aug 28, 2018 at 18:00