0

I have connected a GFCI 15A to a 20A breaker although all outlets have the typical 15A NEMA. Whenever I turn it on it trips if any devices are connected. If I disconnect everything it doesn't trip. Any ideas on why this may be happening?

Without the GFCI (when I remove it and put a regular outlet) everything operates normally.

4
  • Are you sure you have the Hot & Neutral on both Line (back to the breaker) & Load (connecting to the other outlets) are connected the right away? Also, any outlet with hot/neutral reversed (should never happen, but it does...) could cause a problem. Are you sure "any" devices? Do you have a simple device - e.g., a nightlight - that you can test with another GFCI to make sure it is OK and then test with this GFCI, one outlet at a time? Aug 27, 2018 at 0:23
  • The line and load lines are correct. This GFCI won't work if they are not correct (I know because I initially put them the wrong way). I thought it was the surge protector, so I removed and put another one. It worked for a while then tripped again. When the surge protector was on the off, no tripping. Then I would turn it on and it would trip. I tried several devices and all seemed to trip the GFCI. Does it matter if a 15A is on a 20A breaker if I am not drawing more than 15A. Also does it matter than all devices try to suck power at once? (although even one device did the same.
    – Michael
    Aug 27, 2018 at 0:33
  • 2
    Shoot us a photo of how the receptacle is wired. Either it is a line/load issue, or one of your devices has a ground fault. You would troubleshoot the latter by plugging in only one device at a time. It does not matter if all devices draw at once, that is normal. Aug 27, 2018 at 0:33
  • 1
    Even though you are sure you have line/load correct, there still could be a problem with one of the chained load outlets. Try disconnecting load and plugging devices ONLY into the GFCI outlet directly and see if it trips. Aug 27, 2018 at 0:55

0

Your Answer

By clicking “Post Your Answer”, you agree to our terms of service and acknowledge that you have read and understand our privacy policy and code of conduct.

Browse other questions tagged or ask your own question.