I have old-school delta 3 phase (no neutral 240v) service to my shop that has 60 amp fuses on the main. I'd like to hard wire a new machine (max 30amp) about 40 feet away by running #6 wire in conduit to a non-fused 60 amp safety switch that would sit next to the machine. Would this be a proper approach or Should I consider a 60 amp safety switch installed with 30 amp fuses? Should I do something else entirely? Is #6 AWG the correct size wire for this run? I need a little bit of voltage drop because this is a 220v machine with a top end limit of 242v and im measuring 243v at the panel. I'd rather not have to add a buck boost transformer for barely being over voltage limits on the machine. Thanks, Max
Edit: It's high leg delta with no neutral (this property is a 100 year old egg ranch). Machine is 220V / 60 Hz 3 Phase / 15 KVA (7.5hp). A disconnect would be nice because I'd like to leave it disconnected when not in use to protect the electronics. I'd also like it in case something happens with the machine and I can't stop the machine at the control panel