Got a 30 year old fixer-upper recently. Lights dim in house when using garbage disposal or blow dryer. Lights almost turn off when new AC comes on. Had electrician and electric co-op out and they didn't see any problem, only saw a few loose wires. When we had power outage and were using a generator the lights still dimmed when using garbage disposal. Have been slowly replacing old plugs and switches. Don't know where to go from here?

  • Welcome to Stack Exchange. Right now stop replacing plugs and switches. It can't help, and it might hurt by introducing new problems you are not ready for (e.g. if you run into an MWBC, dual-served, split, etc.) Solve the big problem first. For now, focus on surveying what you do have. Lotsa pictures, backs of boxes, service panel, whole nine yards. Then talk to us, and/or school yourself up on this stuff – Harper - Reinstate Monica Aug 7 '18 at 1:56
  • What size is your service, how many square feet is this house, what's the amp rating on the AC, and do you have any other large electrical appliances? (such as a range, electric dryer, or electric water heater)? – ThreePhaseEel Aug 7 '18 at 1:58
  • 1
    Also, how is the transfer equipment in your house set up? – ThreePhaseEel Aug 7 '18 at 2:00
  • 2,100 square ft. We have an older Sub Zero refrigerator, electric oven that is very rarely used, older Jenn-Air four burner ceramic cooktop, new water softner, washer. Everything else is on propane. Get back to you on the rest. – Mike Aug 7 '18 at 3:41
  • Put a voltmeter across the two hot wires in the panel and measure the drop in voltage when the a/c condenser comes on. If there is excessive drop, then check the connections and the lines all the way to the pole. – Jim Stewart Aug 7 '18 at 12:53
3

Almost every time I had a service call where lights are dimming and don't seem to be related (such as they are not on the same circuit). I always found a broken neutral and I usually found it on the service drop. If you are replacing receptacles and switches because they need replacing then that's OK, but its not going to fix your problem. You need to look deeper into the wiring and start checking out neutrals and grounds and possibly where a ground is being used a neutral. This happens most frequently if the original wiring has been disturbed such as in a remodel area of the dwelling.

This can be a long and drawn out process. That's why I would start at the service drop and the grounding electrode system. Take a good look where the service drop neutral is connected at the bracket and see if that is where the conductor has broken by wind movement and such. Then inspect the entire triplex drop to see if some insulation is nicked or broken off of the hot conductors and see if it has shorted and burnt the neutral in half.

Good luck