I have a GFCI outlet in my garage which is about 4 feet off the ground. I have a couple work lights plugged into it which can only be turned on and off by plugging/unplugging them. I have recently just been using the "Test" and "Reset" buttons on the GFCI outlet to turn the lights on and off. It's a lot easier than unplugging both plugs and later having to bend down to pick them up off the floor and plug them in again.
Can doing this a couple times a day do any damage to the GFCI outlet or to anything plugged in to it?
13
    I don't have a definitive source, so I'm not posting an answer, but I cannot imagine how one could ever consider using a device in a manner other than for how it was designed and intended would be a good idea. Aug 6, 2018 at 17:48
    @TheEvilGreebo you can’t imagine that at all? Not even a teeny tiny bit? Aug 6, 2018 at 17:55
    They might not be rated to the same magnitude of switching actions. A GFCI might only be rated for 100 actions over its life (3 times a year for 30 years). Where as a wall switch might be rated for 100000 actions over its life (10 times a day for 30 years)
    – Dan D.
    Aug 6, 2018 at 17:59
  • @Marathon55 for a safety device such as this? No. It's meant to intervene and prevent an electric overload - not for routine daily use. Buy a flipping switch. Aug 6, 2018 at 18:01
  • I understand that GFCI outlets are not intended to be used this way, and I understand that it's possible and may be the case that the GFCI buttons are not sufficiently durable for frequent use. I understand that if that is indeed the situation, I should not use it like a light switch. But that conclusion is built on a premise which is precisely what my question is asking: Is it in fact the case that GFCI outlets are not durable enough for this kind of use? Aug 6, 2018 at 18:33
Certain GFCI+receptacle devices are rated for this purpose.
Use one of those.
There are GFCI devices whose buttons are specifically labeled Off/Test and On/Reset. The reason the "off" and "on" are there is because these devices are built and rated to be on/off switches using the GFCI function. The difference between these and regular GFCIs is these are made for many, many cycles. However, these are difficult to find (especially on the Web, where plain GFCI results bury them) and you will probably need the assistance of an electrical supply house to locate them. One example is a Leviton 8590-RB, however that's a deadfront and you'd want one with sockets. Leviton calls it a switch-rated GFCI.
enter image description here src
If you're fitting a deadfront GFCI to gain this functionality, just mount a box next to the receptacles and put the GFCI there, using the LOAD terminals on the deadfront to feed the receptacle(s).
Far easier to find is the GFCI+receptacle w/ switch device.
Typically on these, the switch is two pigtails. The GFCI+receptacle uses all 4 terminals (LINE hot/neutral LOAD hot/neutral) plus ground, of course. In this case you would not use Test/Reset to turn the load on and off, you'd use the switch. The switch and its load can be placed on the LOAD side of the GFCI protection (carefully).
    Can you provide an example? Aug 6, 2018 at 21:51
  • @manassehkatz Read the stack's guidelines, SE is not a "shop for me" site. So I have been reluctant to be prodded into doing a "product hunt" for you. As it turns out, it's fairly hard just because of the way Google works, and so the best search heuristic is probably visiting your local electrical supply, which is something I am unable to do for you. Sep 4, 2018 at 0:20
  • Your updated answer provides plenty of information now - a specific "buy this" isn't needed, just more than the original one-liner. +1 Sep 4, 2018 at 0:40
  • Installed a GFCI + receptacle a while back. It's really the best way to go, if you can manage with one outlet.
    – Edwin Buck
    Sep 4, 2018 at 17:17
Get an Add-on Switch
I 100% agree with all the others who said "don't do this". The good news is that there is an easy solution. Get a outlet/switch designed to plug into another outlet. Something like BindMaster 3 Prong Grounded Single Port Power Adapter with Red Indicator On/Off Switch, 1 Pack. There are plenty of different brands and styles available, including multiple outlets, WiFi remote control and many other options.
Also note that using a GFCI test button as a switch is very different from using an ordinary circuit breaker as a switch. As I understand it, while using an ordinary circuit breaker as an ordinary on/off switch is often not recommended (and in some situations may even be a code violation), there are at least some circuit breakers which ARE designed to be fully capable of frequent switching use. A GFCI test button is quite different - it actually produces a fault equivalent to a dangerous situation (but within the GCFI module so that it is safe to do so) in order to trigger the GFCI circuit. The result if everything works as expected is that the outlet is turned off. But that is a side-effect and NOT the direct result of pressing the test button.
As noted in another answer, there are some GFCI devices that either include an separate On/Off switch or are switch-rated. Those are certainly options as well, though they may be harder to find (i.e., may require going to an electrical supply house rather than Amazon or Home Depot or Lowes).
The TEST and RESET bottons on a GFCI outlet are not designed for use as a light switch or load switch. Constant usage as such will stress it's internal mechanism such that it may not function properly when called upon actually in it's ground fault trip mode.
If you want to see for yourself then take apart a GFCI outlet and a light switch and see how much more complex and how many more moving parts there are in the GFCI.
