5

My current oven just plugs into a big outlet in the wall. It's a giant three-pronged outlet. But all I need to do to get the oven to work (when it works) is to plug it into the outlet. I am now ordering a new oven online, since the old one has broken. They offer an installation service, but money is tight and I don't want to buy it if not necessary. I have people to help me lift the oven if it's just about lifting the oven, and people to take away the old oven. But will there be electrical issues to deal with, or will the new oven just have a plug and plug into the wall like the old one?

7

In most cases when you purchase a free-standing electric range, you'll be required to purchase the appliance cord separately. The sales person should ask if you need a 3 or 4 prong cord, at the time of purchase.

NEC Article 250.140 Frames of Ranges and Clothes Dryers. requires 4 prong receptacles and appliance cords to be used in new installations, but allows 3 prong receptacles to be used if the following conditions are met.

1) The supply circuit is 120/240-volt, single-phase, 3-wire; or 208Y/120-volt derived from a 3-phase, 4-wire, wye-connected system.

This will almost always be true in a residential setting.

(2) The grounded conductor is not smaller than 10 AWG copper or 8 AWG aluminum.

It's not likely your wire will not meet this condition (unless it's really old).

(3) The grounded conductor is insulated, or the grounded conductor is uninsulated and part of a Type SE service entrance cable and the branch circuit originates at the service equipment.

Again, the supply cable will almost always meet this condition in residential.

(4) Grounding contacts of receptacles furnished as part of the equipment are bonded to the equipment.

This just means that if there are receptacles on the range (I havn't seen this in many years), they must be bonded to the chassis (which should have been done by the manufacturer).


Plugging in a new electric range will not require the circuit to be brought up to current codes, so you should have no problem using a 3 prong appliance cord (in most situations).

It's a good idea to get somebody that has some experience with electrical work to install the cord, since improper installation can lead to injury, fire, and death. The basic idea is that you don't want to restrict conductivity in any way, so you'll want to make sure the terminals are tightened to the proper torque (a conductive paste is sometimes applied to insure adequate conductivity).

While you may be tempted to save a few bucks using the old appliance cord, this is usually not the best idea. Over time the cord may become brittle or develop corrosion, which can both lead to increased resistance, which leads to excess heat buildup, which leads to failure and/or fire. It's not worth the risk, spend the ~$20.00.

Make sure you read the manual before installing the range, and follow any and all manufacture instructions.

2
  • 2
    Re mechanical installation: In many (most?) areas, the range must be installed with an anti-tip device -- basically, a bolted-down bracket that one of the back feet slides into, so if you rest a child-sized roast (or roast-sized child) on the oven door the whole thing can't come crashing forward. Straightforward, but easiest done by someone who's done it before. Another possible argument for tossing them a few bucks and having them deal with it.
    – keshlam
    Sep 5 '14 at 18:46
  • 1
    @keshlam good point.
    – Tester101
    Sep 5 '14 at 18:53
0

The first and most pressing issue is that your receptacle is a three wire and your stove will come with a four wire plug.

5
  • Old code only required two hot wires and a neutral new requirement is for two hot,one neutral and a ground.Similar to how old outlets had only two prongs and now they have three.It is a safety concern.
    – mikes
    May 22 '12 at 2:02
  • Some stoves are direct-wired as well. You can also likely easily swap out the chord with a 3 prong easy enough. SHOULD you? Well, I'll leave that up to you. I, myself haven't seen the 4-pronged ones yet. Something I need to look into. (Granted, it's probably not much harder to swap the 3 prong outlet with a 4 prong, so you might as well do that instead)
    – DA01
    May 22 '12 at 2:47
  • It's not likely that you'll have to upgrade to a new 4 prong receptacle if you have an old 3 prong. You are not modifying the circuit in any way, so you are not required to bring the circuit up to current code. In most cases when you purchase a freestanding range, you'll be required to purchase the appliance cord separately. You should be given a choice between 3 and 4 prong.
    – Tester101
    May 22 '12 at 14:43
  • @mikes If you are going to reference codes, please provide the article numbers. Codes can often be interpreted many ways, and are not always correctly stated on the internet.
    – Tester101
    May 22 '12 at 15:20
  • Basically, this is like grounded and ungrounded outlets. New 240VAC outlets in the US generally have to be 4-prong -- two hots, neutral (because it's fairly common for some of the circuitry to run off just one phase, at 110VAC), and safety ground. Stoves are generally designed to be "double insulated" and safe to run without a safety ground, so there isn't a requirement to upgrade existing outlets... but that's why the bias is now toward 4-prong as the default.
    – keshlam
    Sep 5 '14 at 18:49
0

Most electric stoves do not include the "pigtail" cord that connects from the stove to the outlet. So a typical replacement would go something like this.

  1. Remove old stove from house
  2. Remove old pigtail from old stove
  3. Unbox new stove
  4. Install old pigtail on new stove
  5. Move new stove into place (level with leveling feet as required)
  6. Enjoy.

The basic answer to your question is that if you have a person or two to help you move the stoves, then the installation service is definately optional.

1
  • 2
    Not always a good idea to use the old appliance cord.
    – Tester101
    May 22 '12 at 15:15

Your Answer

By clicking “Post Your Answer”, you agree to our terms of service, privacy policy and cookie policy

Not the answer you're looking for? Browse other questions tagged or ask your own question.