A 14/3 NM-B cable is run from the main breaker panel. The black wire is connected to one 15 amp single pole circuit breaker and the red wire is connected to a second adjacent 15 amp single pole circuit breaker. Are any of the following acceptable according to the National Electric Code? If so, do the handles of the two circuit breakers need to be tied together using a handle tie approved by the manufacturer of the circuit breakers?
- Single duplex receptacle in a one-gang electrical box
- Black wire to the top brass screw terminal
- Red wire to the bottom brass screw terminal
- White wire to one of the silver screw terminals
- Ground wire to the green screw terminal
- Tab connecting the two brass terminals broken
- Tab connecting the two silver terminals intact
- Two duplex receptacles in a two-gang electrical box
- Black wire to the top brass screw terminal of the first duplex receptacle
- Red wire to the top brass screw terminal of the second duplex receptacle
- White wire to the top silver screw terminal of the first receptacle
- Separate insulated white wire from the bottom silver screw terminal of the first receptacle to the top silver screw terminal of the second receptacle
- Ground wire pigtailed to the green screw terminal of both receptacles
- Tab connecting the two brass terminals intact on both receptacles
- Tab connecting the two silver terminals intact on both receptacles
- Two duplex receptacles in a two-gang electrical box
- Black wire to the top brass screw terminal of the first duplex receptacle
- Red wire to the top brass screw terminal of the second duplex receptacle
- White wire pigtailed to the top silver screw terminals of both receptacles
- Ground wire pigtailed to the green screw terminal of both receptacles
- Tab connecting the two brass terminals intact on both receptacles
- Tab connecting the two silver terminals intact on both receptacles
Please reference and/or quote the National Electrical Code.
Reason for question: I recently assumed responsibility for maintenance in a small office building that was constructed in the late 1990s or early 2000s. While adding a new outlet, I noticed that the existing panel makes extensive use of 14/3 NM-B cable where the black wire is connected to one 15 amp single pole breaker, the red wire is connected to a second 15 amp single pole breaker, and the handles of the two breakers are not tied together. Based on other issues I have found, I have a suspicion that the wiring is not compliant with the current National Electrical Code.