So I have a contractor installing a gas furnace where I used to have an electric furnace. I am ending up with a 60a circuit that is not needed anymore. I want to take that circuit and install a subpanel so I can run two or more 15 or 20a circuits off it. Should be able to do that no problem. But where I am confused is instead of having a black and red wire I have a black a white and a bare wire. How do I wire that into my panel?
    Is replacing the wiring run an option here, or would only having 120V be a problem for that matter? – ThreePhaseEel Jun 28 '18 at 1:42
    can you settle for ONLY powering 120V circuits off that panel? – Harper - Reinstate Monica Jun 28 '18 at 1:43
  • Ya that’s all I want is 120 like two or three 15 or 20 amp 120 circuits. – Chad Barker Jun 28 '18 at 2:49
  • @ThreePhaseEel I think replacing the wire would be really hard it’s a long run and it’s finished from start to end. – Chad Barker Jun 28 '18 at 2:51
    @ChadBarker -- what make and model is your main panel? – ThreePhaseEel Jun 28 '18 at 2:56
Make this a 120V only subpanel
Since the original circuit was 240V-only (hot, hot, ground), you're short the neutral wire needed for having both 120 and 240V at the old furnace's location. Since you only need 120V here, though, what you can do is install a 120V-only subpanel; however, that limits you to 50A as 120V-only (by design) subpanels don't come in larger sizes, and trying to use a larger subpanel gets confusing, what with the potential for skipped slots and all.
You'll need a GE THQL1150 breaker (to replace the THQL2160 that's in there right now), a TQLFP1 filler plate to fill the hole left by the other pole, a Square-D QO24L50TTS panel for your subpanel, a suitable NM clamp for the cable coming in, and appropriate QO single pole or QOT double-stuff branch breakers in 15 and 20A, as well as a torque screwdriver or torque wrench that goes up to 50 inch pounds or so as all lugs must be torqued to their manufacturer specification (110.14(D) in the 2017 NEC). Replace the THQL2160 with the THQL1150 (with the main off) -- the black wire that landed on the THQL2160 lands on the THQL1150's lug, the white wire that landed on the THQL2160 gets moved over to land on the neutral bar (torque it to spec too!) as it will be a neutral now, not the other hot leg, and the bare wire stays put as it will continue to be a ground. Snap the TQLFP1 into the hole in the deadfront left where the other half of the THQL2160 was.
Once this is done, leave the new branch breaker off, button the main panel up, and turn the main breaker back on. You can then mount and install the QO24L50TTS in an appropriate spot; once it's mounted and the cable fed in through a KO and secured, you then can terminate the black wire from the cable to the main lug, the white wire from the cable to a lug on the neutral bar on the far right, and the bare wire from the cable to a lug on the ground bar on the far left. Make sure to torque the connections to spec; there will be no bonding strap or bonding screw to pull, as the QO24L50TTS is not suitable for use as service equipment to begin with.
Then, you can install the appropriate OQ or QOT single pole breakers (QO115/120 or QOT1515/1520/2020 depending on the mix of 15 and 20A circuits you need, you can get 4 circuits max using double-stuffs in this panel) and wire up your 15 and 20A circuits to the subpanel. Note that if you want ground-fault or arc-fault protection here, it will probably be easiest to use a short conduit nipple over to a box with a deadfront GFCI, AFCI, or DFCI in it instead of crimping your circuit count with a GFCI, AFCI, or DFCI breaker.
  • Wow that’s very detailed. Thank you! This will leave a gap in my main box correct? If so I guess just get a spacer to put back in? – Chad Barker Jun 29 '18 at 0:49
  • @ChadBarker -- it will, you'll need a TQLFP1 spacer to fill it – ThreePhaseEel Jun 29 '18 at 1:03
  • Or another breaker. Breakers hooked to nothing make exemplary blanking plates, and are useful if you ever add a circuit, which blanking plates are not. Now TPE, is there a code prohibition on simply using every other slot on a 120/240 panel or splitting the one hot and feeding both panel legs? – Harper - Reinstate Monica Jun 29 '18 at 20:16
  • @Harper -- using every other slot on a 120/240 panel isn't wrong, but it is potentially confusing to the next bloke. Feeding both busbars in parallel is...also potentially confusing (in a worse way, even). – ThreePhaseEel Jun 29 '18 at 22:14
  • I have the panel you suggested above ordered because I couldn’t find it anywhere locally. I have a quick question however is this 120 only box so there is only one positive lug? I guess what I am asking is will I still have to skip slots as it only has two that’s not ideal. – Chad Barker Jun 30 '18 at 12:40