We got a new roof about four ago. The attic is unfinished. It's a split level home, and hot as Hades upstairs.
Unfortunately, the roofers didn't consider attic ventilation. They installed a ridge vent, but the only intake is a gable vent near the peak of the roof. Now we realize that hot air stays at the bottom of the attic in that scenario. So we need to add ventilation at the bottom of the attic. Our soffits are not vented. Seems to me the options are to vent the soffits, or to add a shingle-over intake vent along the lower edge of the roof (then seal up the gable vent). Is either of these options preferable for a relatively new roof? We live in DC.
  • If you go with soffi vents (I would), make sure you take into account how many square feet of vents you need. A general rule-of thumb is to take the square footage of your attic / 150, e.g. for a 1500 sq/foot attic you'd need 10 square feet of soffit vent. Also, watch that you don't have attic insulation blocking the vent.
    – raterus
    Jun 26, 2018 at 18:53
I would add soffit vents. If it's wood soffit it's fairly easy to cut the holes with a small rotary saw or an oscillating multi tool. Then screw on prefab vents from any outlet supply. If it's aluminum soffit I've replaced solid panels with vented also and you could space them out and put in as only as many as desired. If it's aluminum fascia on front then removing the fascia first makes removing and reinstalling panels is a snap. Just first remove the aluminum fascia (on front) by pulling the bottom nails with pliers. I always like to screw the alum fascia back on with small stainless Phillips screws.
But if it's wood fascia that usually hangs down past the soffit in front, it becomes more problematic. I don't want to try and explain that to you other than give you a heads up that application can be more of a problem replacing alum soffit panels.
Oh and if the gable vents are not leaking in blowing rain, just leave them, they will just give more top level air escape. I see no need to seal up the gable vent unless you see evidence of gable vents taking in water in a blowing rain (some do, some don't) If that is not a previous problem then just leave them. The will have no negative effect on ventilation in any option scenario.
You say, “Unfortunately the roofers didn’t consider ventilation.” Actually, it’s not an option. It’s required by code. I’d cancel the check and have them return to finish the job. (See ICC R806.)
Your attic is required to have ventilation at 1/150 the area of the attic. (See ICC R806.1.) So, If your house is 24’ x 40’ then you need 24’ x 40’ / 150 = 6.4 sf.
However, there is an exception that allows 1/300 the area if between 40% and 50% of the ventilation is in the upper third of your attic. (See ICC R806.2)
There is another exception that deals with your vapor barrier, but you need a Class I or II installed on the warm-in-winter side.
Did they get a Building Permit?
  • If the roofers installed ridge vent, they did their job. They're not going to be expected to refurbish the soffits in the process.
    Jun 26, 2018 at 19:49
  • @isherwood I disagree. They’re required to comply with the code...not just a part of the code. They could have (and should have) installed the correct ventilation. There are other types of vents they could have used, like roof jacks, etc. The code is looking for cross ventilation and just installing ridge vents does not comply.
    – Lee Sam
    Jun 26, 2018 at 20:41
  • I'm sure you do. :P Soffit venting is the best solution in this case, and roofers don't usually get into that. I'm not sure what's to argue about.
    Jun 26, 2018 at 20:48
  • @isherwood How are you sure?
    – Lee Sam
    Jun 26, 2018 at 20:53
Another option is to put an exhaust fan in your attic, on a thermostat. Which type of fan would depend on the construction of your roof. There are even solar powered attic fans.