0

It seems I lost a power from one of phases feeding the panel. The pen tester proofs that. It's interesting if I reset the main switch, the power comes back. If I put any appliance (be it a small light bulb) the power disappears on the same phase until main switch is turned -> off -> on.

I was wondering someone has any theories what could be the issue?

enter image description here

  • 1
    Do you have the service panel cover off? Make sure to shut off every 240V breaker or it can give you false readings. – Harper - Reinstate Monica Jun 21 '18 at 14:56
  • I disconnected every 240v breaker and capped the wires inside. – bioffe Jun 21 '18 at 14:58
  • Have you checked on the supply side of the main breaker or just the output side. Breakers do go bad, I have had quality main breakers loose a leg. Sometimes turning the breaker on and off 10+ times with all the breakers turned off will clean and reseat the hammers in the breaker, if this works be prepared to buy a new breaker and replace or you will have the same problem in the future. – Ed Beal Jun 21 '18 at 16:31
  • Nope. Supply side of the main switch is beyond my comfort level as an average Joe homeowner. I am trying to understand science of this phenomena before I pay $000 dollars to electrician for a piece of advice. – bioffe Jun 21 '18 at 18:36
  • 2
    If it's on the supply side of the meter, it's the power company's responsibility and the bill will be $0.00. Calling them is free, I would try it. – Harper - Reinstate Monica Jun 21 '18 at 21:14
2

Most likely scenario: your main has a connection to the bus inside of the panel that distributes the power to all of the other feeder breakers. That connection is likely bad / corroded / burned, something that is creating high resistance. With no lod, your tick tracer picks up that there is voltage present, but as soon as you apply a load to it, the resistance causes the voltage to drop to effectively zero. Resetting the main breaker wiggles it a little to make just enough of a connection to satisfy that tick tracer, but that's it.

This is your life and safety involved here, the next phase of development of this problem may be a fire. you need to call an electrician.

  • I was thinking along the same line. Thanks for the clear explanation. If it is a corrosion issue, how come it happened in one day? I would rather expect this issue to become from incidental to systematic. I will try to deal with the main switch now. – bioffe Jun 22 '18 at 17:43
  • It could have been incremental, but one day, you hit the threshold. But you're right, that points more toward damage from it being loose and there is a build-up of carbon from arcing that has now reached a point of high resistance. – JRaef Jun 22 '18 at 22:59

Your Answer

By clicking “Post Your Answer”, you agree to our terms of service, privacy policy and cookie policy

Not the answer you're looking for? Browse other questions tagged or ask your own question.