This is a normal 15A 125V wall outlet in my dining room. It consists of 2 black hot wires, 2 white neutral wires, and a bare copper ground wire. Here is the problem. If I wire all 4 wires to the 4 side screws on the receptacle, the circuit breaker for this section trips. If I just wire one hot and one neutral to either the top or bottom, there is no problem. The ground wire is always connected. What is the problem here and how can i fix it? Thanks.
    More information would be helpful: 1 - Did this work in the past and stopped working recently? 2 - Is this a replacement outlet or the original? 3 - Does the circuit breaker that trips have GFCI or AFCI protection? 4 - Are there other outlets that work/don't work on the same circuit? – manassehkatz-Moving 2 Codidact Jun 5 '18 at 2:43
    What voltage do you measure between the two black wires here, if you have a voltmeter or other sort of tester than can measure it? – ThreePhaseEel Jun 5 '18 at 2:54
    @ThreePhaseEel I was thinking maybe MWBC with previous outlet top/bottom on separate legs and new outlet top/bottom on same circuit, but couldn't figure out how to test it - but measuring voltage between blacks would do it. – manassehkatz-Moving 2 Codidact Jun 5 '18 at 2:57
  • I believe this worked in the past. I'm not sure. Its a replacement outlet, but its identical to the original. I don't believe there's any GFCI or AFCI protection. The other outlets work fine. This one works fine if just one set of black and white wires are connected. If I connect both sets the circuit breaker trips. I don't have a voltmeter. Suppose I do should the two black wires have identical readings? thanks. – J. Kauffman Jun 5 '18 at 3:03
  • @J.Kauffman -- how many breakers do you need to turn off to make it so there is no power on either set of wires? – ThreePhaseEel Jun 5 '18 at 3:06
There are three typical reasons to have two black/white/ground cables going into an ordinary duplex receptacle:
1 - Separate circuit for top and bottom to get more power - i.e., 15A on each outlet instead of 15A for the pair together. In this situation the receptacle would have the tabs broken off, cables supplying power coming from two different circuits, possibly sharing a neutral as a multi-wire branch circuit (MWBC) or possibly just two entirely separate circuits. Connecting both cables to a new outlet with the tabs in place would trip the breaker as described. However, the pictures you posted of the old receptacle clearly shows the tab (at least one side) intact.
2 - One outlet on a switch and one "always on". This is often done to have a light plugged in and controlled with a switch while still having some power always on for other devices. In this case typically, but not always, the power would all come from one circuit. The tabs would be broken off. The result, if you connected a new duplex outlet without breaking off the tabs would typically be that both outlets would be always on and the switch would be ineffective - but the breaker would not trip. There is also a possibility that a switch loop could be messed up here, causing part of the problem.
3 - One cable "in" and one cable "out". This is very common. You have a chain of receptacles, each with two cables, except for the last one. If that's the case, the preferred method (as I have learned recently) is to pigtail and only use one pair of screws on the receptacle, but using both one set of screws for each cable, with the tabs in place, would work just fine. But that would not explain the breaker tripping, and you would also have other receptacles or lights or something not working any more.
Take a look at the old outlet and the new outlet. The new outlet has a connection tab on each side between each pair of screws. If the same tab on the old outlet was broken off then the old outlet was fed either by two separate circuits or one receptacle was switched. If that is the case then you can either use one set of wires and cap (wire nut) off the other set of wires, or you can break off the tabs from the new outlet and wire one pair to the top and one to the bottom.
However, if this is the situation then:
  • If there were two circuits then you should have TWO breakers that need to be turned off to get both circuits turned off, not one. If you really only needed to turn one off then there is something else going on. If you really needed to turn off two breakers and didn't realize it, then you are very lucky.
  • The wires should be in clear pairs. (I believe you have confirmed that with the later pictures). If it is not 100% clear which white goes with which black then STOP. If the two circuits are a multi-wire branch circuit then the neutrals are shared and it doesn't matter. But if they are two totally separate circuits then this matters a lot as the neutral and hot have to match.
After all of that, I am a bit baffled. A tester to check voltage would really be helpful here. There could be hot/neutral swapped somewhere along the line (dangerous, but would explain the problem) or something else.
Also, as Harper noted, the backstabs are a very bad thing. I don't think they are the problem here (except perhaps why the original outlet went bad) but they are frequently a source of problems. But with my understanding of the nature of the backstab problems, that wouldn't explain the problem you are having with the two cables tripping. In any case, do NOT use backstabs on any new receptacles, and if you disconnect any backstab wires, reconnect them only to the screw terminals.
The key thing now is to figure out whether both cables are hot or not. If they are both hot then you should only be using one with tabs in place. If only one is hot then you need to figure out where the other one goes to check for problems at the other end.
| improve this answer | |
  • the old receptacle is exactly the same as the new one. The tabs are intact. Inside the wall are two large separate insulation wires: each containing a black wire, a white wire, and a ground copper wire. The ground copper wires are twisted together from each separate insulation. Anyway its an old house so probably a lot is screwed up. So one set of hot and neutral wires is enough to power both the top and bottom plug? Thanks a lot. Also the other outlet that is affected by the same breaker switch has 4 wires back stabbed into the respectable. Exact same wiring setup. That one works fine. – J. Kauffman Jun 5 '18 at 3:22
  • @J.Kauffman Correct that one set is enough. But what I (and I think ThreePhaseEel and Harper) am trying to figure out is why you have two cables. Are the tabs intact on the OLD receptacle? I'll explain more in my answer. – manassehkatz-Moving 2 Codidact Jun 5 '18 at 3:25
    so if i just use 1 set of white & hot wires, and cap the other set, there won't be any safety concerns right? worst case scenario something i don't know about doesn't get power? – J. Kauffman Jun 5 '18 at 4:17
    As far as I know, that would be fine. – manassehkatz-Moving 2 Codidact Jun 5 '18 at 4:18
    @manassehkatz - You should clean up the part of your answer at the beginning where you explicitly say that two wires coming to the outlet means there have to be two circuit breakers. This is not true in many cases for half switched outlets that may very well be on the same circuit. The point #3 that you added later also invalidates these initial comments. – Michael Karas Jun 5 '18 at 12:14
Mana' is doing a great job with electrical answers, so I'll go another way.
It's the backstabs
Perhaps due to unclear markings, you are connecting supply hot and neutral to backstabs on the same side, creating a short from the outset.
Regardless, a rule of backstabs is that they are single use. If you are pulling the wires out or popping the release, the internal spring is now "sprung" and will not make contact reliably. You get four of these springs in a 50 cent socket, what can you expect? I could see internal damage happening too, which may also be the problem.
Backstabs are not made for homeowner troubleshooting, they have a single purpose: high speed assembly by builders. It's so a builder can wire 7 houses a week instead of 5. So there's no reason for a homeowner to pay the reliability penalty that is the reason most of us refuse to use them.
Try a new receptacle and the side screws or screw-to-clamp types, which have unlimited uses. Do not back out the screw too far, the screw are captive and "liberating" them will strip the hole or ruin the clamps.
Pigtail the receptacle
I really mean leave the receptacle out of it, by using wire nuts to connect the blacks and whites in the box. If this trips the breaker, it means the downline circuit has a serious problem, or is not meant to be connected this way.
At that point, follow the directions in my comment colon connect the receptacle only to one of the incoming cables. You'll know which one is correct, the receptacle will work.
In this Arrangement, when you are ready to attach the receptacle, you put 6-inch wires on each of the screws, and join each one to its wire nut.
  • I agree 100% with the warning about backstabs. But as I understand it, this was a new outlet using screws to replace the old one (which was using backstabs). Of course, if it comes to troubleshooting by way of any of the other outlets in the circuit (which if one is backstab, the others are probably too) then the backstab issue will become very relevant. – manassehkatz-Moving 2 Codidact Jun 5 '18 at 14:49