1

From my understanding, in San Francisco, CA, there is a code requirement that you cannot obstruct an area within 18 inches of a fire sprinkler. What is meant by obstruction? Say, you installed one of these: http://rakks.com/wall-mounted-standards/

  • 3
    Just a standard, or would you attach something to it? – fixer1234 May 23 '18 at 8:11
  • Is this sprinkler head ceiling mounted or wall mounted? – ThreePhaseEel May 23 '18 at 11:47
  • It is wall mounted. @ThreePhaseEel – Sargun Dhillon May 23 '18 at 15:33
  • The standard would be attached to shelves -- but the shelves would be more than 18 inches away from the sprinkler. The purpose of having the standard there is so it can go along the entire corner. @fixer1234 – Sargun Dhillon May 23 '18 at 15:34
  • Is this a house/duplex/townhome, or an apartment/condo building? – ThreePhaseEel May 24 '18 at 2:37
1

The standard itself is fine, just be wary of what attaches to it

Since a standard that is less than 1" deep off the wall is going to be shallower than a sidewall sprinkler's escutcheon, it will not "prevent the pattern from fully developing", therefore NFPA 13 8.10.7.2 does not apply:

8.10.7.2.1.1 Continuous or noncontinuous obstructions less than or equal to 18 in. (457 mm) below the sprinkler deflector that prevent the pattern from fully developing shall comply with this section.

However, you do need to be careful with how you set up your storage to avoid running afoul of the intent of 8.10.7.3 with the storage itself. I would follow the same 18" rule enforced for standard sidewall sprinklers by 8.7.6:

8.7.6 Clearance to Storage (Standard Sidewall Spray Sprinklers). The clearance between the deflector and the top of storage shall be 18 in. (457 mm) or greater.

1

It depends on the shape of the spray and the rating of the sprinkler head.

Sprinkler heads are rated for various situations. Based on the head rating, the sprinkler engineer can layout a pattern that “covers” the spaces based on the occupancy rating. That is to say, one kind of head will work in a narrow residential hallway, while another type is rated for business areas with tall shelving.

Very complicated. I’d contact the sprinkler installer. Their name will be on a metal plate chained to the “riser” or where the water enters the building.

  • This building has had at least 2 large companies work on the sprinkler systems, including contractors through Webcor. They're not particularly forthcoming about things... – Sargun Dhillon May 24 '18 at 6:03